In the  4-conductor connector, two contacts are the "hots" (that is, 
each is 120  either side of neutral), one is neutral, and the fourth 
must be a green  equipment ground wire that bonds the equipment 
enclosure and backbox. That  is the only way to legally (and safely) 
use a 4-wire 240/120 volt  circuit.

73, 

Jim K9YC 



Right you are Jim!!  One must understand that a "4" wire system here  is 
correctly referred to as a 240/120 volt circuit, not simply a 4 wire 240 volt  
circuit.  Also, as far as NEMA goes one should use the proper  plug/receptacle 
combo for the system they are matching.  Some plugs have  "4" pins and are 
240/120 volt recognized some a "4" pin and 3 phase  recognized.  They have 
different configurations, but should be used in the  right combinations.  One 
of the 
most common mistakes I have seen in  electrical wiring done by the "ham" vs the 
"electrician" is when one adds a  sub-panel for the  ham shack distribution 
of AC power.  Many do NOT  separate the bonds from the neutrals in the 
sub-panel which is a code  violation.  Lou