For planning purposes, one must keep in mind
that 'balancing out' the strong influence of 60 Hz 
AC flowing in lines that they wish to 'filter' that in 
a 240/120 V  '2-phase' configuration (with neutral) 
that *minimum* current flows on the neutral line 
at the service drop/gen when the load: 

a) is across the 'outer' lines (240 V) supply lines or 
b) is equally balanced between each of the two 120 V 
   lines (to neutral).

Other factors such as motor-starting (LRA - locked 
rotor amperage) and motor running current draw (lagging
power factor) will change this 'balance' too, as will 
non-linear loads like power supplies, et al.

Jim P  /  WB5WPA  / 
 

----- Original Message ----- 
From: "Jim Brown" <jim@audiosystemsgroup.com>
To: "RFI List" <rfi@contesting.com>
Sent: Tuesday, March 22, 2005 6:47 PM
Subject: Re: [RFI] Honda Generator RFI


> On Tue, 22 Mar 2005 16:29:10 -0800, Clay Curtiss  W7CE wrote:
> 
> >For the latter, I'm not sure which cores would be best.
> >I need to filter 30A at 240V.
> 
> A good commercial line filter at the generator is probably be a good 
> idea. Not all are created equal, so study the specs carefully. You 
> want to ground the filter to the generator with very short leads. 
> 
> As to cores -- they are likely to saturate under load if you put 
> them on individual conductors, so plan on putting them on the paired 
> cable so that the total field is small (that is, the hot is 
> cancelled by the return). Used this way, the cores will attenuate 
> common mode radiation from the line. 
> 
> There is an applications note on my website that you may find 
> helpful. 
> 
> http://audiosystemsgroup.com/SAC0305Ferrites.pdf 
> 
> Note that the data in this applications note applies specifically to 
> small signal applications where saturation and heating of the core 
> do not occur. Both will reduce the effectiveness of the ferrite. 
> 
> Jim Brown  K9YC
> 
> 
> _______________________________________________
> RFI mailing list
> RFI@contesting.com
> http://lists.contesting.com/mailman/listinfo/rfi
> 
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

<Prev in Thread] Current Thread [Next in Thread>