Re: [RFI] Grounding of A Rinnai RC80HPI Tank Less Water Heater

To: rfi@contesting.com
Subject: Re: [RFI] Grounding of A Rinnai RC80HPI Tank Less Water Heater
From: Jim Brown <jim@audiosystemsgroup.com>
Reply-to: jim@audiosystemsgroup.com
Date: Fri, 08 May 2015 18:11:04 -0700
List-post: <rfi@contesting.com">mailto:rfi@contesting.com>
The short answer to your question is that all of that equipment MUST, by Code (which carries the force of Law) be grounded by the "Green Wire" of the circuit that feeds power to it. In addition, that connection must be bonded to all exposed metal parts on the equipment.

But there's a lot more to it than that. First, a connection to earth is NOT part of a solution to RF noise problems, but that bonding IS important. That's something I would check.


Given the poor condition and/or sloppiness of the power wiring, I would look into that, and consider replacing it. It's also possible that something is mis-wired there. If you do replace it, buy twisted triplet or twisted quad cable from the electrical supply store or the big box store. Twisting is great at reducing RFI. 240 volt power must be fed by the two "hot" conductors, plus the Green for Ground. Make sure that Green is used for GROUND, and NOT for power. Make sure that Neutral is NOT used for Ground. Make sure that Green is not used to carry power.

And from your description, I would mistrust the capabilities of the contractor for that tankless heater and find a smart electrician to do this work if you are not qualified to do it yourself. I suspect that the source of the noise is control circuitry for that unit, but you might be hearing it because of bad/wrong wiring.

73, Jim K9YC

On Fri,5/8/2015 4:59 PM, Wm.Glenn Pearson wrote:
Hi,

I have a major rfi problem to which I have devoted enormous time
investigating. I will shortly prepare a query to ask the group once I can
get my thoughts organized. But I have made several discoveries which may or
may not be important. I have a Rinnai RC80HPI Tank Less Water Heater which
was installed several years ago. I discovered that it is not grounded except
through its outlet ground. The product manual indicates that NEC, ANSI/NFPA
70 be referred to for grounding (separate ground)  it or not.

Even more interesting is that my plumber used long drop cord (sold by Home
Depot) to its final destination at an outlet box wired to my breaker panel.
The actual 3 conductor AC cable from the unit is rather poor looking now.
Furthermore, he had wrapped excess drop cord cable around a nearby natural
gas conduit and an electrical feeder line. When I move the wrapped bundle
the water heater started making "squawking noises." I rerouted the drop
cord.

This led me outside to investigate our 3 gas Heat and Air Systems to see
whether or not they were grounded. There is an outside sub breaker box for
the system with a single fed back to my breaker panel. Today a service man
was by for the seasonal inspection and so I asked him whether or not the
units should be tied to a earth ground. He indicated they were depending on
the ground in the wire back to the panel box.

The next item along this same line is that we have a commercial
de-humidifier under our house as well. It too is fed by a long drop cord and
plugged into the same circuit as the water heater. Its distance from the
panel box is about 20 feet. The same is true for the water heater as well.

Over all I have been going thru the process of cutting house power and
monitoring for problem circuits and devices as I turned each back on. I must
note that unplugging the heater and de-humidifier has no effect on resolving
my problem.

I am of the mind for each device, a separate circuit should have been run
with its own outlet box. I am unclear with regards to separate grounding of
the HVAC units. Your thoughts and advice is most appreciated. Hopefully
shortly I will be able to fill in more of the details of my killer rfi
problem.

Thanks,

Glenn Pearson, WU2G