On 9/6/2012 4:36 PM, GARY HUBER wrote:
Jim, just verifying my understanding of the following;

Green (Grounded) and White (Neutral) bond ONLY at the MDP (Main Distribution Panel). Green wire must run with neutral to main or supplemental panel and MAY also be grounded elsewhere but those grounding points MUST be bonded to the system / site / premise ground in accordance with the National Electrical Code.

Right.

The key here is that there MUST be ONE, AND ONLY ONE bond between neutral and Ground (the Green Wire) in any System, and it MUST be where the System is established. A "System" is established 1) at the Service Entrance (where power comes into the building) and 2) at a transformer. A typical residence or small building has only one System. Larger buildings may have several systems.

One of the most common wiring errors made by electricians is to have additional bonds between Neutral and Green. This most often happens two ways. First, when you buy a breaker panel, there's a bonding screw that automatically bonds the Neutral bus to the Ground bus (the Panel chassis). That's fine if it's the Main Panel, but if it's a Sub-Panel it MUST be removed, and sometimes that isn't done. The other way that extra Neutral bonds happen is in older laundry equipment.

By contrast, the Green wire can be taken to earth as many times, and in as many places, as you like.

BTW -- someone correctly observed that in many localities, most wiring is three conductor cable with black, white, and bare copper for ground. Yes, that bare copper is "the Green Wire." It's called the Green wire partly because of history, partly because when wiring is in conduit or other metal raceway the dedicated ground wire must be Green, and partly because, in North America, the ground conductor in portable cables is usually Green.

73, Jim K9YC