Jim Brown wrote:
> On Tue, 03 Nov 2009 17:00:11 -0500, Mike wrote:
>
>
>> Would it be a reasonable idea to pull a ground out of the breaker box,
>> and tie it to the tower and bring it into the shack also to tie all this
>> together?
>>
>
> Yes, BUT: Don't use that circuitous route through the attic, because
> lightning won't follow it. Lighting will take the lowest impedance path,
> which is usually the shortest one. DO bond everything together by the
> shortest practical path, more connections are better. DO bond the tower
> directly to the electric service ground by the shortest practical path.
> Also, be sure to also bond together the telephone ground, and the CATV
> ground, the satellite dish ground with the electrical ground and the tower
> ground.
>
> 73,
>
> Jim K9YC
Thanks, Jim -
My thinking was that the route through the attic IS the shortest
distance. I assume(yeah I know) the house came with a connection
between the power entrance ground and the breaker panel through the attic.
73, Mike NF4L