The prior comments indicate that having MOVs at the service entrance is the
way to go to get "whole house" protection.  There are a number of commercial
products available.  I use the following, and have had excellent results:

These are Cutler-Hammer products and model numbers:
CHSPMAX (AC power lines)
DHW4PT (4 Telco lines)
DCXCAB2 (2 cable/sat coax lines)

------------------ Wes Attaway (N5WA) ------------------
1138 Waters Edge Circle - Shreveport, LA 71106
    318-797-4972 (office) - 318-393-3289 (cell)
        Computer Consulting and Forensics
-------------- EnCase Certified Examiner ---------------

-----Original Message-----
[] On Behalf Of
Sent: Friday, March 19, 2010 6:31 PM
Subject: Re: [TowerTalk] Shack wiring

Hi Jim,
I still don't get it (maybe because I am dumb). At my service entrance  is 
a protector that connects has two MOVs, one from each leg to ground.  Ground

in this case is the same as neutral At the water pump is also a protector  
that has MOVs frm the two legs (the pump is a 240 V pump) and ground. In the

 shack I have a protector that connects MOVs from neutral AND the hot 120 V 
leg  to ground. It also incorporate a protecting circuits for my phone, it 
has two  gas discharge tubes between the line and ground.
Should I disconnect al MOVs that are connected to ground ??? As I wrote to  
you earlier, my house has had two registered lightning hits (and possible a 
 couple of more we don't know about) and everything survived.
Can anyone describe the failure mode that makes the MOV from the hot leg to 
 ground bad?
Hans - N2JFS
In a message dated 3/19/2010 1:33:50 P.M. Eastern Daylight Time, writes:

Hi  Dick,

I don't know "the Soft-Start kit" or it's application, so I can't  comment 
what I've said here. But MANY products are designed with  serious 
mistakes. The "pin 1 problem" is a glaring and very  common example -- it 
hum, buzz, and RFI. Putting an MOV between  line and safety ground is 
another one 
-- it can blow up equipment! The  only safe place for an MOV (or other 
protector) in the power  system is at the main service entrance where power 
into the building  from the street. This is the so-called "whole house" 
and it's a  very good idea if done well.  


Jim K9YC

On Fri,  19 Mar 2010 17:22:37 +0000, RICHARD SOLOMON wrote:

>Are you  saying we should not use the ones that come with the Soft-Start 
kit  ??

>73, Dick, W1KSZ

>> From:
>> To:
>>  Date: Mon, 15 Mar 2010 22:50:45 -0700
>> Subject: Re: [TowerTalk]  Shack wiring
>> On Mon, 15 Mar 2010 21:34:10 -0400, wrote:
>> >A good surge protector has  three MOVs, one from each leg and one 
>> >the  legs.
>> WRONG! An MOV from Phase (hot) to Ground (Green  Wire) is more likely to 
>> UP equipment than protect it. To  understand this, see my earlier post 
>> this. 
>> 73,
>> Jim K9YC