> Wouldn't it be feasible to simply open up the existing three-way  devices 
> and remove the two legs that are undesired?
Jack,
Although not optimum (through a slow discharge of surge current to neutral), 
cutting the L/G, and N/G MOVs and leaving only the L/N MOV in a pre-existing 
3-mode SPD is certainly a possibility.  I see nothing that would violate UL 
1449 -- but I'm no expert with UL standards.
One point not mentioned before (and I think to Pete's point) -- I would not 
install any SPD device on a branch circuit without first installing a 
whole-house SPD.  I don't think that's a requirement from the single-mode 
SPD manufacturers, just my own philosophy for what that's worth!
Paul, W9AC