>The big hazard in the 3 wire situation with some load current in the
>common ground/neutral conductor is that when the ground wire fails, 120
>volts WILL be found on the case.

Probably the larger issue in the 3-wire 120/240V configuration (e.g., 
unmodified Alpha 70/77 series) is if neutral and ground are tied at the 
equipment -- and neutral accidentally lifts above ground potential, then the 
chassis becomes hot with 120v-circuit current and that current will find its 
way back to its source via BNC, PL-259, RCA and any other connector that is 
grounded to the chassis.

In fact, left unmodified without going to 240V/120V 4-wire service and power 
cord, that current is still dividing between the equipment's neutral/ground 
point and the grounded chassis connectors.  It's a good thing that 99+% of 
the time, the neutral/ground point on the equipment is of much lower 
impedance back to the service panel than the chassis connectors!

So, left unmodified, older amps with 120V blowers are still a safety concern 
if they are serviced by only 3-wires.  There's only one right way:  Pull 
4-wire, 240/120v service into the shack with proper conductor and breaker 
size, and replace the 3-wire power cord with a 4-wire power cord.  The 
latter part is easy with Alpha 70/77 series amps.

Paul, W9AC 