At least here, 240 volt single phase is from the centre point of a Y connected 
transformer. The outside ends of the windings all have 415 volts between them 
i.e. if you wire them a to a delta load, the load is a three phase 415 volt 
load, and it seems the system in Chile is similar, but the voltages are 
different. Here distribution is at 400kV, 275kV, 132kV, 66kV, 33kV, 11kV and 
there may still be some places with 6.6kV or 3.3kV. It's now mainly 11 and 33kv 
distribution in rural areas. Our local expert is G4LDL, who is this week 
commissioning and in charge of the testing of a 90MVA 132kV primary transformer 
- rather bigger than what we are all accustomed to! I gather that in the US, 
the 'Pole Pig' is a single phase transformer with a primary connected between 
one phase and ground, which is also the star point of a Y connected transformer 
secondary. The secondary is then a 240 volt winding, with grounded centre tap, 
giving 120 - 0 - 120.

 I presume the Thai 4 wire system is three phases and a Y neutral. By 
transforming to 240 or 220 or whatever and not grounding one side, what 
prevents the line floating up? - for instance, you could have one wire at 300 
volts above ground and the other at 540 volts above ground. I would expect that 
measuring the volts from each side to a good ground will show one pin somewhere 
 around a few volts above ground and the other 240 or so volts higher. Having 
typed  all this and checked what has come in, I see Manfred has exactly the 
same thought.

Ideally, Charly would use a HV tester to test the insulation between input 
wires and chassis (with the amp unplugged) and from the transformer primary 
terminals to chassis. It should be very high. As the amp doesn't use the 
chassis as a return for anything connected to the AC line, then the fusing of 
one side shouldn't make any difference although the main fuse should then feed 
other fuses so that fault tolerance is built in. What does need doing is to 
ensure a good external ground is connected to all the station equipment, and 
then it won't matter which way round the amp is plugged in.

73

Peter G3RZP