To: <amps@contesting.com>
Subject: [Amps] Amplifier Relocatable Power Tap
From: "Paul Christensen" <w9ac@arrl.net>
Date: Fri, 24 May 2013 10:34:02 -0400
List-post: <amps@contesting.com">mailto:amps@contesting.com>
Since constructing the W8ZR StationPro II (SPII), I've been thinking about ways 
to best manage AC power distribution for my desktop amps.  The SPII is a 
station accessory designed to easily route RF, audio, digital communications, 
and control cabling between three transceivers and three amplifiers.  Until 
recently, I've been crawling under the operating table to switch my amplifier 
AC power cables.  I use one branch circuit consisting of a 30A OCPD (breaker) 
and a #10/4 run to a 30A Twist-Lock receptacle.  4-wire cabling is used since 
the older Alphas make use of a neutral for the blower.

To feed AC power into three amps, I had several choices:  (1) add more branch 
circuits; (2) add a J-box in the wall and spit one branch circuit that feeds 
more than one receptacle; or (3) construct a relocatable power tap (i.e., a 
240/120V version of a multiple outlet strip).   I decided against options 1 & 2 
since the house will one day go to a new owner and I didn't want to add even 
more wall trauma.  Further, the NEC limits option #2 to 20A circuits but as it 
turned out, 20A service will be fine for my future needs.

Option #3 became the plan but what does UL have to say about 240/120V RPTs?  UL 
1363 sets the standard although another UL provision addresses portable power 
distribution of the type generally found at construction sites.  Even though I 
will not mass-produce these RPTs , I wanted to know how close I could come to 
making one that is 100% UL 1363 compliant.  I got pretty close.  In fact, it 
complies but for the fact that the PVC J-Box has permanent mounting holes.  UL 
1363 states that any physical mounting must be effectuated without the use of 
tools.  Typically, we see home RPTs with mount blocks designed to slip over 
screw heads so that the RPT is easily attached and removed without the use of 
hand tools.  

UL 1363 has a significant limitation: use of an RPT is limited to 20A service 
and ALL device connectors must be of the same type and current rating.  This 
had a "trickle up" effect.  Since the RPT is limited to 20A, then so are the 
connectors.  But now we move from UL to the NEC since the NEC is a premise 
wiring standard and not a products wiring standard.  As the plug is limited in 
size to 20A, then the mating receptacle must be 20A.  Finally, NEC 210.21(B) in 
this application states that the serving OCPD must match the receptacle rating. 
 In essence, use of the 20A RPT forced a re-design of the branch circuit from 
30A to 20A components although wiring is allowed to stay at #10/4. 

130A-rated copper bus bars are used to distribute service into three outputs.  
You'll see this in the photos.  It was actually possible to forgo the bus bars 
and use jumbo #10 winged wire nuts to join four #10 conductors together.  
Kinda' scary, but they're used all the time.  However, almost all of the wire 
nuts are not rated for fine-stranded portable power cable.  I really didn't 
consider this a viable option.  

A larger J-Box could have been used to install panel receptacles rather than 
pig-tails but the box size gets pretty large when you consider space needed for 
panel receptacles.  Short pig-tails also allow the use of different styles of 
20A plugs/receptacles, provided they remain the same type.

My amps are all legal-limit and 20A service is adequate.  For many members on 
this list, this RPT device would not work for obvious reasons.  The #10 cabling 
helps to reduce voltage drop losses over an 80 ft run.  If MOV/TVSS devices are 
considered for secondary surge protection, place only between Line 1 and Line 
2, and one each from the line to neutral -- with no MOVs going to the grounding 
conductor.  Even then, I would not use MOV/TVSS unless "whole-house" protection 
is first used at the service entrance as the primary surge protection device.  
This is another reason why adding a neutral may make sense even if your present 
amp only requires 3-wire service and no neutral.  Adding the neutral also 
ensures that you can properly use older Alpha and Henry amps in the future.

In a nutshell, here are some features of the RPT:

1) 1 x 3 device, designed for either 3 or 4-wire powering (240/120V);
2) #10 wiring and #10 hardware used;
3) Heyco compression connectors;
4) Nickel-plated copper bus bars (with protective covers) rated at 300VAC and 
130 amps;
5) Dual fuseholders with 20A ABC ceramic fuses;
6) Dual neon light AC power indicators; and
7) 20A Hubbell Twist-Lock connectors used on all cable ends.

Some images in the links below.  Photos taken before wiring the neon lamps:

http://tinyurl.com/oswgsfh
http://tinyurl.com/oqpkg2f
http://tinyurl.com/qeszuft
http://tinyurl.com/qjabggu
http://tinyurl.com/nlo9pk6

Paul, W9AC