What is interesting to me are all the different opinions on one method vs. 
another.  All I can do is add yet another opinion.

I live in NE Indiana where the soil is nothing but solid, hard stinkin clay. 
When I was installing my 3 towers the first order of business was installing 
3 ground rods for each.  I also wanted to install 3 rods near the QTH 
entrance at my metal panel.  First, let me say that I was shocked at how 
difficult it was for me to get them into the ground.  Second, I was using a 
combination of 1/2" steel rods (copper coated) and a bunch of 10' long 1/2" 
and 3/4" copper pipe.  Using the sledge hammer on the copper pipes quickly 
resulted in mushroomed ends which had to be cut off with only several feet 
being driven into the ground. This, regardless of how careful I was hitting 
the rods. The steel rods did better but were stopped about half way down 
leaving 4 or more feet out of the ground.

I'm over 6' tall and 250 pounds and am not afraid to work with a 
hammer.....let me tell you, I just could not get the rods down. The clay was 
so hard and dense it just was not working.  Soon I was trying the hydro 
method on some of the 3/4" copper pipes. For my clay it just didn't work. It 
did end up making a terrible mess as the countless gallons of water were 
just emptied out around the rod at the ground surface.  Remember, this is 
clay so all that water stays on the top where is makes a fine mess.  I then 
tried to cut the drilling end of the copper pipe at a 45 degree angle and 
must have lifted and driven down the pipe (with water flowing) several 
hundred times before finally giving up. The driving end under ground will 
get mangled up as well sometimes making it nearly impossible to pull back 
out.

Next came the heavy steel pipe over the copper pipe with end cap idea.  This 
managed to get the pipes down a bit but eventually the ends of the copper 
still mushroomed.  If you don't stop and cut off the bad portion it will 
become stuck inside the heavy steel pipe and you won't be able to get it 
out.  Some of the copper pipes bent right after the steel pipe and once this 
happens all you can do is cut it off at ground level and start a new one.  I 
even tried to carefully add water to the hole (slop area right around the 
rods) every day for over a week thinking I might be able to "soften" up the 
ground a little with no difference whatsoever.

The only thing that worked, for me, and several others have mentioned this, 
was to use an impact hammer. In my case I was able to borrow a real 
industrial electric Jack-Hammer. Without any attachments the opening of the 
hammer will let you slide in a 3/4" copper pipe.  Using a step ladder I was 
able to drive every rod into the clay in about 15 minutes time. It was very 
hard work as the hammer is large and weighs almost 100 pounds.

Sorry for being long-winded but I wanted to share my experience in case 
someone is in the same predicament as I was.  I hope this can save someone a 
bunch of time and a lot of sore back muscles and frustration.

73,
Gedas, W8BYA

online image gallery at  http://gedas.cc
e-mail address at  w8bya@w8bya.com
web page at  http://www.w8bya.com

----- Original Message ----- 
From: "Buck - N4PGW" <n4pgw-list1@towncorp.net>
To: "'towertalk reflector'" <towertalk@contesting.com>
Sent: Sunday, June 12, 2005 1:49 AM
Subject: Re: [TowerTalk] Copper pipe for ground rods?


>I have heard a lot of pros and cons about hydro-drilling.  I believe that
> people who use one over the other will not notice what they have or don't
> have until they compare the two.  If you hydro-drill, your ground will
> eventually pack back around the pipe.  If you drop a solid rod, you will 
> add
> a lot of elbow grease.
>
> If money is an issue, use the copper pipe and the water hose.  If not, 
> then
> plan on buying a short piece (about 24") of heavy-gauge steel pipe with
> threads and an end cap.  The heavy pipe will make for a rod hammer that is
> easy to use.  Just place the ground rod where you want it to go in with 
> the
> pipe on top.  Lift the pipe and let go.  It will stay over the ground rod
> and the weight will drive the pole into the ground.  If you are feeling
> really good, life the pipe and pull it down hard over the rod while 
> holding
> onto the pipe.  This could make the job go faster.  Around here, the pipe 
> is
> usually able to do the job.  When the pipe gets close to the ground, use a
> sledge hammer.
>
>
>
>> -----Original Message-----
>> From: towertalk-bounces@contesting.com [mailto:towertalk-
>>
>> Alan,
>> I have used both the copper clad steel rod, and copper 3/4" copper pipe 
>> on
>> several grounding applications in different soil textures. (from rocky
>> clay to loam)
>> Aside from the obvious cost advantage of  copper pipe, I really prefer 
>> the
>> pipe for it's ease of installation.  If you have a source of pressurized
>> water and a hose, it is a piece of cake to hydro-jet a 10 foot section
>> into just about any soil including dense clay or fiable rocky material
>> including granular volcanic material on the the Big island of Hawaii.
>> (about 3" minus)
>> Once you try this method, you will never go back to any other.
>>
>> Jon
>> K6EL
>> --
>>
>>
>> > Alan,
>> >
>> > Depending on your soil, you probably won't be able to get it in as deep
>> as a
>> > real ground rod before you start to smash the copper; at least that was
>> my
>> > experience with one I use for an electric fence around my tomatoes (I
>> have
>> > Labradors).  It only went in three or four feet, but it works fine for
>> my
>> > purpose.
>> >
>> > 73 - JC, k0hps@amsat.org
>> >
>> >
>> > -----Original Message-----
>> > From: towertalk-bounces@contesting.com
>> > [mailto:towertalk-bounces@contesting.com]On Behalf Of Alan NV8A (ex.
>> AB2OS)
>> > Sent: Friday, June 10, 2005 8:24 PM
>> > To: towertalk reflector
>> > Subject: [TowerTalk] Copper pipe for ground rods?
>> >
>> > Any reason not to use copper pipe for ground rods instead of the
>> > outrageously expensive copper-clad steel ones that have almost doubled
>> > in price over the last year or so?
>> >
>> > They may not comply with the NEC, but they would only be supplementary
>> > to the existing NEC-compliant grounding system anyway.
>> >
>> > Alan NV8A
>> > _______________________________________________
>> >
>> > See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless
>> > Weather Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with
>> any
>> > questions and ask for Sherman, W2FLA.
>> >
>> > _______________________________________________
>> > TowerTalk mailing list
>> > TowerTalk@contesting.com
>> > http://lists.contesting.com/mailman/listinfo/towertalk
>> >
>> >
>> > _______________________________________________
>> >
>> > See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless
>> Weather
>> > Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with any
>> questions
>> > and ask for Sherman, W2FLA.
>> >
>> > _______________________________________________
>> > TowerTalk mailing list
>> > TowerTalk@contesting.com
>> > http://lists.contesting.com/mailman/listinfo/towertalk
>> _______________________________________________
>>
>> See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless
>> Weather Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with
>> any questions and ask for Sherman, W2FLA.
>>
>> _______________________________________________
>> TowerTalk mailing list
>> TowerTalk@contesting.com
>> http://lists.contesting.com/mailman/listinfo/towertalk
>>
>
>
>
> _______________________________________________
>
> See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless 
> Weather Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with 
> any questions and ask for Sherman, W2FLA.
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk@contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
> 


_______________________________________________

See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless Weather 
Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with any questions 
and ask for Sherman, W2FLA.

_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>