On 5/25/13 1:02 PM, Eugene Jensen wrote:
Drilling holes in conduit for drainage is not a good ideal. It going to be full of 
water in time. As long as your trench is 18 " or deeper you could use  UF #6-2 
with ground  to keep the voltage drop under 3%. And the run your control/Rf cables 
in the same conduit, It you using hard line just bury it in the trench. 73 and good 
luck with your tower project. Gene AA4VX


CHeck your local codes, if you're concerned. around here (Thousand Oaks), UF is not allowed for direct burial. Underground has to be in a raceway (code speak for conduit). There's various burial depths depending on the kind of conduit (plastic, thinwall metal (EMT), or thick wall metal) and whether it's under a concrete slab or similar. The depth is all about damage to the wires (since frost is a non issue).