Honda generators put out trash as a common mode signal on the green
wire. It is NOT acceptable to choke the green wire, but it IS acceptable
to choke all three conductors. Thus, the solution is winding turns
through #31 or #43 cores, following the winding advice in my Choke
Cookbook for RG8-size cables. We use Honda 2000i generators on FD and
California QSO Party county expeditions, and these filters work.
Conventional power line filters do NOT suppress this noise, because the
green wire goes straight through them. Yes, they do spec "common mode
rejection," but their definition of common mode is the voltage between
neutral and green, which is not common mode from an RF point of view.
73, Jim K9YC