> Looking over the wiring diagram for the control box after the fact,
> I am questioning why UST did not just simply wire the two limit
> switches in series, then just use the UP/DOWN toggle switch to break
> the connection between the series-wired limit switches and the motor.

With the limit switches in series you would not be able to move the
tower off either limit.

It would be better to use a 4PDT center off to switch hot/neutral or
a using separate switches - one to control direction the other to
switch power.  The problem with the two switch version is the need
to remember to stop motion before reversing direction.

73,

   ... Joe, W4TV


On 2015-07-02 12:34 AM, k2cb@comcast.net wrote:
I recently had an interesting issue with my HDX-589MDPL tower.  I am
posting my experience, hoping it saves someone from a potentially
catastrophic event. We had a rather intense storm rip through the
Philadelphia suburbs last week, so on the side of caution, I made the
wise decision to run outside and lower my tower down somewhat before
the storm approached my area to the east.  Good decision - we had
numerous trees down and a few broken power poles, resulting in a 30
hour power outage.......... But the tower and antennas made it
through unscathed.

However, as I was retracting the tower, once it reached my desired
level, I went to place the UP/OFF/DOWN toggle switch in the OFF
position.  However, the tower kept moving in the downward direction.
In a panic, I flipped the switch up, then back down to the OFF
position, which made no change. Fortunately the GFI outlet was within
reach, so I simply tripped the GFI test button to stop the tower.
Upon resetting the GFI outlet, even with the switch in the OFF
position, I heard a loud buzz emanating from the tower motor. Not
good. However, if moved the switch to the UP position, the tower
would move up, but going back to OFF, the tower would still continue
moving up.  I had to pull the power cord or trip the GFI outlet to
stop the tower.

Fortunately,  I had the tower down to a safe level. The storm was
fast approaching, so I called it a day and figured I would
investigate further the next day...........

In the meantime, I placed a call to US Tower. One of their
electricians kindly returned my call, explained the design of the
control box, and emailed me a block diagram.

The next day, once power was restored, I did some troubleshooting.
While the tower was moving in the downward direction, the lower limit
switch was tested, and the tower was able to be stopped by manually
engaging the lower limit switch.  However, when performing the same
test in the upward direction, the upper limit switch had no effect,
and the tower continued to move upward. Fortunately I performed these
tests with the tower somewhere around halfway up, so it was not much
of a concern at the time. However, had I decided to fully extend the
tower, the results could have been disastrous!

Next, I decided to pull the cover off the control box on the side of
the tower.

The motor and limit switches are controlled via the toggle switch,
which is a 3PDT center off switch made by Carling Technologies.  Two
of the poles are used to reverse the phasing of the motor direction
control leads, and the third pole is used to supply the main neutral
feed to the motor. The main hot lead is hard wired to the motor at
all times. The center of this third pole feeds the motor, the up side
connects to the return from the upper limit switch, and the down side
of the switch connects to the return from the lower limit switch.
Both limit switches are hard wire fed from the AC supply neutral. The
limit switches each provide their own neutral path back to the toggle
switch. The toggle switch simply selects which limit switch is in
effect at the time. The upper limit switch is in effect when the
switch is in the up position, and the lower limit switch is in effect
when the switch is in the down position. When the tower is NOT at
either limit, both limit switches are conducting a neutral return
back to the toggle switch.

Now here is where things get bad real quick - in my case, the common
terminal and the lower terminal of the third pole of my switch failed
in a SHORTED condition!  Basically, the motor was connected to
neutral at all times via the lower limit switch. Thus the reason the
tower would move in the proper direction once the switch was thrown
up or down, but would not stop once turned off. Also, if left in the
OFF position, and power was applied to the AC cord, the motor would
buzz due to lack of direction control lead supply, while main hot and
neutral were now immediately present at the time of plug-in.

Fortunately, I was moving in a downward direction when the switch
decided to fail shorted in the DOWN direction. Had I fully lowered
the tower, the lower limit switch would have still taken effect and
broken the neutral path.  However, had I decided to raise the tower
with this switch failure condition, the upper limit switch would have
been of no use, as the lower limit switch was still in the circuit,
supplying the neutral return at the same time as the upper limit
switch!  I surely would be telling a different story at this point!

I tested further and made sure the limit switches themselves were ok,
and that the motor was still functioning properly. I then began the
search for a replacement toggle switch.

The next day I ran over to my nearest Grainger Supply warehouse,
where I was able to pick up an exact replacement switch.

For future reference, the switch is a CARLING TECHNOLOGIES HM254-73
3PDT ON-OFF-ON SWITCH.    It is also available from Mouser for a few
bucks less before shipping, but I wanted it right away.

I installed the switch in short order. UST did a nice job of using
spade lugs on all of the wires, and the switch uses brass screw
terminals. $25 and a few hours later I had the tower tested and back
to normal operation.

Looking over the wiring diagram for the control box after the fact, I
am questioning why UST did not just simply wire the two limit
switches in series, then just use the UP/DOWN toggle switch to break
the connection between the series-wired limit switches and the motor.
This way, both limit switches are always inline when the circuit is
completed, and in the event of a switch failure such as I just
experienced, both limit switches would still function at all times,
regardless of motor switch direction, thus avoiding a potentially
catastrophic event. If the toggle switch were to fail shorted, at
least either limit switch could break the neutral return path
regardless of the switch direction.

Summary: Do yourself a favor and regularly test the toggle and limit
switches as part of your routine maintenance
inspections.........................

Eric K2CB


_______________________________________________



_______________________________________________ TowerTalk mailing
list TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>