They're called "concrete encased grounding electrodes", and googling
turns up a bunch of hits.
Generally, 20 ft of conductor encased by at least 2" of concrete (on
all sides). either 1/2" rebar (galvanized or not) or AWG4 bare copper wire.
Electrical code NEC250-50(c) is probably your best bet.. The Mike
Holt low voltage handbook (http://www.mikeholt.com/ has a link) covers it.
http://www.iaei.org/subscriber/maagazine/01_d/johnston.htm has a
summary, too, along with some history (Ufer did 24 grounds in Arizona
in 1942, all had resistances <5 ohms at the time, in 1960, the max
reading was 4.8 and min was 2.1.. I'm sure that's resistance at low
frequencies)
One warning on Ufer grounds is that you have to make sure there's no
vapor barrier or liner between the concrete and the soil. (for
instance, the slab under my house has a vapor barrier under the slab,
but not under the footings around the edge, so it works ok.)
I can look up the data in the IEEE-141 spec for grounding and get the
equation if you want more info.