References: [ +subject:/^(?:^\s*(re|sv|fwd|fw)[\[\]\d]*[:>-]+\s*)*\[Amps\]\s+4\s+wire\s+240VAC\s+service\?\s+What\s+to\s+do\s+now\?\s*$/: 32 ]

Total 32 documents matching your query.

1. [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Commander John <crazytvjohn@yahoo.com>
Date: Mon, 4 Apr 2011 08:26:20 -0700 (PDT)
Ok I understand about 4 wire 240 vac service. I installed Code, 10 gauge, 4 wire line to shack and installed a end of line, inline jack. New ameritron amplifier has 3 pin plug on the end. What to do
/archives//html/Amps/2011-04/msg00098.html (6,928 bytes)

2. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Jim Brown <jim@audiosystemsgroup.com>
Date: Mon, 04 Apr 2011 09:34:34 -0700
PLEASE go back and STUDY what I and several others have written several times in this thread, and in the power and grounding tutorial that's on my website. http://audiosystemsgroup.com/publish.htm NE
/archives//html/Amps/2011-04/msg00107.html (7,866 bytes)

3. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "Dick Green WC1M" <wc1m73@gmail.com>
Date: Mon, 4 Apr 2011 13:49:48 -0400
Yes, and the neutral and ground must be isolated in any subpanels as well. However, there's one exception: if the subpanel is more than a certain distance from the main panel (not sure how far), such
/archives//html/Amps/2011-04/msg00113.html (10,481 bytes)

4. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "James R Carr" <n7fcf@hctc.com>
Date: Mon, 4 Apr 2011 12:13:39 -0700
It should be treated as a seperate building. The panel would have it's own main breaker but the neutral would remain ungrouned and the panel enclosure and equipment ground would be grounded to the se
/archives//html/Amps/2011-04/msg00119.html (13,672 bytes)

5. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: TexasRF@aol.com
Date: Mon, 4 Apr 2011 15:22:50 EDT
In a typical sub panel, is the buss bar that is used to common the neutral leads insulated from the box chassis? I have installed a couple of sub panels through the years but never paid any attention
/archives//html/Amps/2011-04/msg00121.html (14,186 bytes)

6. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Al Kozakiewicz <akozak@hourglass.com>
Date: Mon, 4 Apr 2011 15:24:22 -0400
Yes, the neutral bus bar is insulated and separate from from grounding bus bar. You don't bond the neutral and safety ground from the outlet or other device together in the subpanel like you would in
/archives//html/Amps/2011-04/msg00122.html (15,246 bytes)

7. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "James R Carr" <n7fcf@hctc.com>
Date: Mon, 4 Apr 2011 12:29:47 -0700
Normaly it is insulated with the provision of adding a bonding screw to ground it if it is used as a service panel. If it is to be used as a subpanel with an ungrounded neutral, add a ground buss ava
/archives//html/Amps/2011-04/msg00123.html (14,619 bytes)

8. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "Shane Youhouse" <kd6vxi@gmail.com>
Date: Mon, 04 Apr 2011 12:41:31 -0700
The absolute safest method, using old tech 3 wire amplifiers if you have a 4 wire cord is to install a GFCI on each leg of the 220. Use it to plug in a wall wart or reading lamp, keep it balanced. If
/archives//html/Amps/2011-04/msg00126.html (9,905 bytes)

9. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Ron Youvan <ka4inm@tampabay.rr.com>
Date: Mon, 04 Apr 2011 15:43:53 -0400
The neutral buss bar is always insulated, but the screw connecting it to the box is flagged for removal if used as a sub panel. -- Ron KA4INM - Endless Loop: n. see Loop, Endless. Loop, Endless: n. s
/archives//html/Amps/2011-04/msg00127.html (8,960 bytes)

10. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Mon, 4 Apr 2011 15:54:21 -0400
If a sub panel is fed from a breaker in the main panel then it is a sub panel. A sub panel doesn't have to have a main breaker in it. Yes neutral remains ungrounded at the sub panel. YES you DO need
/archives//html/Amps/2011-04/msg00129.html (16,242 bytes)

11. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Mon, 4 Apr 2011 16:03:08 -0400
You need a 220 gfci. Separate gfci's for each side of a 240 line will not work. A gfci looks for a difference in current between the two wires connecting it. 73 Gary K4FMX ___________________________
/archives//html/Amps/2011-04/msg00130.html (11,699 bytes)

12. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Jim Brown <jim@audiosystemsgroup.com>
Date: Mon, 04 Apr 2011 14:07:37 -0700
The issue is NOT distance, but rather creating a separate SYSTEM. A separate system is created by a TRANSFORMER, or by feeding another building. A power system MUST have its neutral bonded to ground
/archives//html/Amps/2011-04/msg00135.html (15,464 bytes)

13. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Jim Brown <jim@audiosystemsgroup.com>
Date: Mon, 04 Apr 2011 14:29:06 -0700
All panels are built with a neutral bus that is insulated from the steel enclosure. In most, there is a large bonding screw that shorts the neutral bus to the enclosure. If the neutral bond is not pe
/archives//html/Amps/2011-04/msg00137.html (9,721 bytes)

14. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Jim Brown <jim@audiosystemsgroup.com>
Date: Mon, 04 Apr 2011 14:47:41 -0700
Read it again, Jim. In Method #1 there is NO ground conductor between buildings, and a neutral bond in both buildings.In Method #2 this IS a ground conductor between buildings but NO neutral bond in
/archives//html/Amps/2011-04/msg00139.html (9,576 bytes)

15. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Doug Renwick <ve5ra@sasktel.net>
Date: Mon, 04 Apr 2011 15:49:30 -0600
I looked at my Federal Pioneer sub panel and I do not see a neutral to enclosure (ground) bonding screw or any where a screw has been removed. Doug _______________________________________________ Amp
/archives//html/Amps/2011-04/msg00140.html (9,854 bytes)

16. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Mon, 4 Apr 2011 17:57:49 -0400
Jim, Your method #1: This method was allowed several years ago but NEC no longer allows this. You must now run 4 wires to building #2 and NOT bond neutral and ground in building #2. that panel is tre
/archives//html/Amps/2011-04/msg00142.html (18,775 bytes)

17. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "James R Carr" <n7fcf@hctc.com>
Date: Mon, 4 Apr 2011 15:13:40 -0700
Then it is designed as a sub panel only. Lots of luck finding Federal breakers now days. Jim N7FCF -- Original Message -- From: "Doug Renwick" <ve5ra@sasktel.net> To: <amps@contesting.com> Sent: Mond
/archives//html/Amps/2011-04/msg00144.html (9,147 bytes)

18. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Doug Renwick <ve5ra@sasktel.net>
Date: Mon, 04 Apr 2011 17:12:04 -0600
No problem finding Federal breakers here in Canada, plus I have a bunch of spares. Doug _______________________________________________ Amps mailing list Amps@contesting.com http://lists.contesting.c
/archives//html/Amps/2011-04/msg00150.html (9,373 bytes)

19. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: Doug Renwick <ve5ra@sasktel.net>
Date: Mon, 04 Apr 2011 17:23:22 -0600
Is this OK? I ran 3 wires (120v only) to a sub panel in building #2. I installed a ground rod at building #2 and grounded the sub panel. I will have to check to see if the neutral is connected to the
/archives//html/Amps/2011-04/msg00151.html (10,596 bytes)

20. Re: [Amps] 4 wire 240VAC service? What to do now? (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Mon, 4 Apr 2011 21:38:02 -0400
Being that it is only 120 volts you have a hot, neutral and a ground wire run out there. You should have the ground wire from the main panel connected to the ground buss in the sub panel along with t