We have three power poles on our land bringing in 220VAC at 200 Amperes. Ther first pole just carriedspower wires, here it splits, like a Y to two other poles. Pole #1 only feeds a water pump through
/archives//html/RFI/2011-01/msg00215.html (8,624 bytes)

2. Re: [RFI] CHECK your grounds. (score: 1)
Author: Jim Brown <jim@audiosystemsgroup.com>
Date: Wed, 26 Jan 2011 14:49:46 -0800
You need to study the fundamental principles of AC power distribution. A GROUND conductor does NOT carry load current -- it's sole function is SAFETY. The current carrying conductors are the Phase an
/archives//html/RFI/2011-01/msg00216.html (8,874 bytes)

3. Re: [RFI] CHECK your grounds. (score: 1)
Author: "K8RI (Roger)" <K8RI@rogerhalstead.com>
Date: Wed, 26 Jan 2011 18:53:54 -0500
I'd add that the green wire is needed for ground fault breakers and outlets to work. Also it causes the fuse or breaker (GFI) to go if there is a short (or leakage current to ground), but over curren
/archives//html/RFI/2011-01/msg00217.html (12,315 bytes)

4. Re: [RFI] CHECK your grounds. (score: 1)
Author: "Dale Svetanoff" <svetanoff@earthlink.net>
Date: Wed, 26 Jan 2011 19:07:55 -0600
Roger, Thank you very much for sharing your very scary experience with the list. It's been my observation over many years that all too many hams either do not practice good grounding or even if they
/archives//html/RFI/2011-01/msg00218.html (16,146 bytes)

5. Re: [RFI] CHECK your grounds. (score: 1)
Author: "KD7JYK DM09" <kd7jyk@earthlink.net>
Date: Wed, 26 Jan 2011 17:27:19 -0800
"The EARTH is a lousy conductor, and should NEVER carry current in a power system. A connection to earth is almost never part of a solution to an RF or noise problem." And yet no concern for the lack
/archives//html/RFI/2011-01/msg00219.html (8,676 bytes)

6. Re: [RFI] CHECK your grounds. (score: 1)
Author: "Rick Karlquist" <richard@karlquist.com>
Date: Wed, 26 Jan 2011 18:20:10 -0800
I don't see why a GFCI circuit should need a green wire to work. It should be able to detect an imbalance between the neutral and phase currents independently of what is going on with ground. Rick N6
/archives//html/RFI/2011-01/msg00220.html (8,288 bytes)

7. Re: [RFI] CHECK your grounds. (score: 1)
Author: Larry Benko <xxw0qe@comcast.net>
Date: Wed, 26 Jan 2011 21:16:32 -0700
Rick, You are absolutely correct. GFCIs only sense the differential current between the HOT and NEUTRAL lines. Any imbalance greater than ~5mA causes a trip. The current that causes the imbalance can
/archives//html/RFI/2011-01/msg00221.html (8,879 bytes)

8. Re: [RFI] CHECK your grounds. (score: 1)
Author: Michael Coslo <mjc5@psu.edu>
Date: Thu, 27 Jan 2011 08:15:57 -0500
I've always thought that way too many things are called "ground". I recommend homeowners who can safely look at their wiring do so. I don't care if it was a "qualified electrical technician" that did
/archives//html/RFI/2011-01/msg00222.html (8,929 bytes)

9. Re: [RFI] CHECK your grounds. (score: 1)
Author: "Paul Christensen" <w9ac@arrl.net>
Date: Thu, 27 Jan 2011 09:42:50 -0500
That's a good practice. I recently changed out all the outlet's in the dining room of a friend's home. Each receptacle contained a combination screw terminal with optional "spring-contact" for quick
/archives//html/RFI/2011-01/msg00223.html (10,120 bytes)

10. Re: [RFI] CHECK your grounds. (score: 1)
Author: Jim Brown <jim@audiosystemsgroup.com>
Date: Thu, 27 Jan 2011 09:17:46 -0800
YES, YES, YES, YES! The use of the word "ground" to describe circuit common, or the chassis, causes MUCH confusion and leads to extensive muddy thinking. That muddy thinking extends to WRONG question
/archives//html/RFI/2011-01/msg00224.html (11,763 bytes)

11. [RFI] CHECK your grounds. (score: 1)
Author: Steve Kurtzman <sparkie001@dslextreme.com>
Date: Thu, 27 Jan 2011 21:09:19 -0800
Some comments regarding US NEC requirements for grounds. You locale may differ. Your main service entrance must be "grounded" to the following grounding electrodes, if present: 1 - Cold water pipe wi