Hello Again,
Trying to establish the loaded voltage output of the plate transformer that
I am going to use with full wave bridge rectification and capacitor
filtering. It is the one that Ten-Tec buys from MCI Limited for the Titan
III. I tried to get some "real life" numbers from somebody on the reflector
but have had no responses.
The transformer itself has a label with the following ratings, two 117 V
primaries and a 2015 V secondary at 1.5A
Tentec claims a 3000 V "no-load" plate voltage on the Titan III.
My calculations are as follows:
Actual Primary Voltage 240 V
Actual Secondary Voltage w/ 240V on primary 2067VAC
2067 x 1.414 = 2923 VDC NO-LOAD
2923 less 10% = 2631 VDC @ 1.5 AMP
Are these calculations correct?
Thanks
Manuel R. Alonso
KC4MNE