Hello Les;
 
I will try to explain some of what might be going on at your location.  Please 
do not take my observations or possible conclusions as a suitable solution or 
design.  There are probably several other factors, which you might not have 
mentioned, that could have a substantial effect upon the opinions expressed 
here.
 
Your situation is much more complicated than a normal house by two factors:  
 
1.  There are several structures, with interconnecting cables.  These  can act 
as independent grounded entities.
 
2. There is a tower, that can increase the likelihood of direct strikes. 
 
Unless exceptional bonding and lightning grounding establishes an 
equi-potential plane, it is possible that you will have to suppress all 
external input and even inter building wiring.  Just running grounds in 
parallel with power or signal conductors may not be able to 
reduce damaging current flow.  I have seen numerous cases of wiring in buried 
metal conduit be unequal to the task of reducing damaging energy in the wires. 
 
>From your description, the most likely problem that you encountered was a 
>ground potential rise involving the pole servicing your location.   
 
The voltage of the location where lightning enters into the soil is elevated 
substantially, together with all nearby equipment.  Despite our efforts, with 
the best ground electrodes, the resistance is almost always too high to avoid 
creating this high driving voltage.  Most electrical codes require either an 
earth electrode resistance of less than 25 Ohms, or use of two ground rods, at 
the service entrance.  The value of 5 Ohms might be achievable in a Florida 
swamp, while over 50 Ohms might be typical in a dry Colorado location.  A small 
lightning stroke current of just 10kA will tend to produce 50kV or 500kV at 
that poor electrode.  I say tend, because there are usually parallel paths to 
share current, and arcing (side-flashing) and other breakdown can also occur 
to limit the voltage.  Keep in mind that double insulated power equipment is 
designed and hypoted at only 2kV to 4kV, so this level of driving voltage is 
easily enough to
 cause failure to most equipment.  Communication wiring is usually susceptible 
at much lower voltages.
 
Architectural lightning protection, which includes rods and wires on the roof 
ridges, needs to include adequate ground bonding to make voltage gradients 
small across the span of equipment and interconnecting wiring.  This is why 
lightning grounding and bonding usually includes a peripheral ground wire 
system.  This seems to be installed at the house, but not the other 
structures. The next technique is to suppress all wire entries to 
the ground system.  Finally, use adequate, however imperfect, earth electrodes 
to drain the current into the soil.  Using the tower grounding as well as 
the power service entry electrode and grounded wire also can augment the 
earthing connections. 
 
Les, you ask "Do I need to connect the two buildings? If so, would a cable 
through the
conduit be safe? Any other suggestions?"  You are already connecting the 
building, with cable.  More connections might increase protection, however the 
following parameters are involved in whether two buildings are separate or 
grounded as one:  Distance of separation of the buildings, the resistivity of 
the soil,  the location of earthing electrodes and peripheral grounds, the 
susceptibility of interconnection wiring, a tower, the height of the 
building or other factors increasing the likelihood of direct strikes.  Off 
hand, with the experience of damage, it is likely that these factors are not in 
your favor, and just installing cables in conduit will very most likely not 
protect the equipment.
 
Not only the lack of a SPG, but the possible lack of earth connection at the 
garage might be a problem for power faults as well as lightning currents.
 
Also, with a tower, I would would hesitate to assume that there was only one 
strike, or that it occurred only at the tree location.  Or will not strike in 
the near future.
 
In response to your comments 
"To prevent these problems in the future, I think the CATV hardline 
should be grounded where it enters. This is easy but probably won't stop 
any surge on the inner conductor. What can be done for that?"
 
NexTek makes an excellent protector with F connectors for 75 Ohm video and CATV 
lines.  Please refer to:
 
http://www.nexteklightning.com/products/Arrestors/Standard/Cable.html

 
This product does contain voltage limiting on the center conductor!
 
The minimum code requirement in most locations is to ground a coaxial cable at 
the entry to a building.  While this does an adequate job of reducing fire and 
electrical voltage risks, it does not prevent damage in many cases.  You might 
actually need protectors when cables transit one building to another, if the 
voltages cannot otherwise be controlled.
 
 
I hope this helps explain some of the possible factors in your situation.
 
George
 


      