Towertalk
[Top] [All Lists]

Re: [TowerTalk] TowerTalk Digest, Vol 127, Issue 27

To: towertalk@contesting.com
Subject: Re: [TowerTalk] TowerTalk Digest, Vol 127, Issue 27
From: Jim Lux <jimlux@earthlink.net>
Date: Thu, 11 Jul 2013 07:05:25 -0700
List-post: <towertalk@contesting.com">mailto:towertalk@contesting.com>
On 7/11/13 5:53 AM, David Robbins wrote:
actually.... you can have great grounding and still get this kind of
damage if you don't equalize the incoming line voltage with ground at
the entrance.  most of this damage was probably from what is called a
back flashover.  this is where the ground potential changes relative
to the power/signal wires due to a lightning strike to a tower or
ground or power line ground.  in these cases the power/signal wires
can be looked at as being at a constant voltage while the ground
potential changes until it flashes over to the signal wire, in the
case of homes this is often through your equipment power supply or
modem on a phone line or cable tv box.  the fix for this is to apply
mov's or other voltage equalizers between the power/signal lines to
ground at your service entrance/single point ground so all the wires
rise and fall at the same time.

Indeed.. a decent voltage clamp at the service entrance will insure that your power lines never go more than, say, 500V from the chassis ground (unless you've got big lightning currents flowing "through" the house or ground). Almost all modern electrical appliances and such can take 1500-2000V between line/chassis.

Your 1950s All-American 5 clock radio, perhaps not.
Your homebrew GaAs FET preamp, perhaps not.



Low voltage stuff can still be damaged by another factor, induced
currents from nearby strikes.  the longer the wiring attached to the
device the higher the voltage.  preventing this type of damage
requires mov or other equalizer on devices inside if they don't have
them built in.  this is where surge arresters in power strips or
ups's can help out since the energy is 'relatively' small compared to
other events.


In order to induce voltages/currents from a changing magnetic field, the victim has to be a "loop" of some sort. Most often, the loop is formed by the "greenwire ground" between the two boxes in combination with the signal wires in the cable. e.g. boxA chassis to threeprong plug ground, through house safety ground wiring, to three prong plug, to box B, to signal wires referenced to chassis, through cable back to Box A, where termination is referenced to chassis. It's pretty easy to get a very large area inside that loop, especially if you're looking at things like network or phone wires running across the house.

If the only interruptions in current flowing in that loop are reverse biased junctions in the components at either end of the cable, you're looking a recipe for damage.

Transformer coupled Ethernet has the transformer insulation in the loop, which helps a LOT.

To a certain exent, double insulated wall warts (which don't require a ground pin on their AC supply) help with this. Now the loop path has to traverse the parasitic C across the transformer windings, etc..

It starts to get more complex when you consider the propagation time for an impulse, but for lightning, the primary energy components are around 1 Mhz, and at that frequency, even a house sized loop is still pretty small compared to 1 microsecond propagation delay.

A overhead power line to a building a mile away, though, with the other half of the loop being the ground between the buildings, and you've got a nice big loop. But also one where the wave propagation needs to be considered.
_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>