>> It is quite common to see
>> mains spikes of 1kV and more
>> on the *primary*
>> side of the transformer.
>> According to ANSI/IEEE
>> statistics, "medium
>> exposure" sites in the USA
>> can expect several hundred
>> 1kV-peak mains
>> spikes per year, and even
>> 5kV-peak spikes at about 1 per year.
>
>Precisely why MOV's or transient
>suppressors should be mandatory in all
>HV psu's.
? For full-wave rectifier, choke-filter supplies, and all half-wave
rectifier supplies, yes. Capacitor-filter supplies and resonant-choke/C
filter supplies have built-in spike suppression, so a MOV is money down
the crapper, except for testing a transformer with no load.
>....
- R. L. Measures, a.k.a. Rich..., 805.386.3734,AG6K,