On 5/4/2021 3:59 PM, Jim Garland wrote:
Our point of disagreement is whether we should connect the "third wire"
in the amplifier power cord to N (my opinion) or to G (K9YC's opinion).
Hi Jim,
I'm not giving an OPINION. I am stating what the LAW says about it,
namely the Electrical Code adopted by local Authorities Having
Jurisdiction (AHJs), virtually all of which are either the National
Electric Code (NEC) (which is a model prepared by a group of experts),
or a local code which is very close to NEC. NEC is revised periodically
(every three years, I think), and local codes may be one or two versions
behind. Last I looked, California was a couple of versions behind.
The only condition in which a Green wire is permitted to carry load
current or is permitted to be bonded to neutral is a "grandfathered"
installation of an appliance that was done before the Code changed to
prohibit it.
The only conditions in which it is permitted (and required) to bond
Neutral to Green are 1) at the service entrance and 2) where a new
SYSTEM is established by the addition of a transformer (and NOT an
auto-transformer).
I just finished working with N0AX on the second edition of his ARRL book
on the topic. Until I retired, I taught courses on Power and Grounding
to contractors installing large scale sound and/or video systems, and
was commissioned to write a "White Paper" on the topic.
http://k9yc.com/SurgeXPowerGround.pdf
73, Jim K9YC