Re: [RFI] New Sears Dryer Draws Current on Green Wire

To: rfi@contesting.com
Subject: Re: [RFI] New Sears Dryer Draws Current on Green Wire
From: Cortland Richmond <ka5s@earthlink.net>
Reply-to: ka5s@earthlink.net
Date: Thu, 10 Nov 2011 14:10:12 -0500
List-post: <rfi@contesting.com">mailto:rfi@contesting.com>
That is the normally only place safety ground and neutral should connect.

 From wikianswers
QUOTE.
.... New installations of ranges and clothes dryers must have a separate 
green or bare grounding conductor.

Now, there is an exception for existing installations. I have put *BOLD* 
emphasis on parts that may apply to your question. The text in brackets 
[ ] is not part of the NEC but explanations added by me.

...only where an equipment grounding conductor *[green wire]* is not 
present in the outlet or junction box, the frames of electric ranges, 
wall-mounted ovens, counter-mounted cooking units, *clothes dryers*, and 
outlet or junction boxes that are part of the circuit for these 
appliances *shall be permitted* *to be connected to the grounded circuit 
conductor [white neutral wire]* if *all* the following conditions are met.

(1) The supply circuit is *120/240-volt single-phase, 3-wire*; or 
208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.

(2) The grounded conductor is *not smaller than 10 AWG copper* or 8 AWG 
aluminum.

(3) The *grounded conductor [white wire] is insulated,* or the grounded 
conductor is uninsulated and part of a Type SE service-entrance cable 
and the branch circuit originates at the service equipment.

(4) Grounding contacts of receptacles furnished as part of the equipment 
are bonded to the equipment *[any built-in receptacles on your dryer 
have a ground connection (green wire) to the metal frame of the dryer]*.

Read more: 
http://wiki.answers.com/Q/If_a_dryer_has_a_green_ground_wire_that_was_connected_to_the_green_wire_on_the_4_prong_cord_what_do_you_do_with_the_green_wire_now_that_you_have_a_3_prong_cord#ixzz1dKa7I5YW
END QUOTE
(smaller):*http://preview.tinyurl.com/7qkf3af*

Cortland KA5S

On 11/10/2011 12:07 PM, ron wrote:
> On 11/09/2011 04:43 PM, Jim Brown wrote:
>> I just had a new Sear dryer delivered and hooked it up per the
>> instructions.  For a four wire service, it calls for neutral to be
>> bonded to green at the dryer. I didn't want to do that (it violates NEC
>> and good engineering practice), so I didn't hook up the neutral, and
>> connected green to the chassis.
>
>
> It defies logic because back at the service panel, the white and green
> share the same connection.
>
> 72
> Ron, wb1hga