This is a followup to the report in our 3830 posting for the CQ 160 CW contest. 
 It is intended as a help for others that might be plagued with a long term, or 
suddenly appearing, power line noise source.  With proper tools and a knowledge 
of what you are looking for, most often positive results can be achieved.

Here is how N5BG and I approached this GIGANTIC noise problem which pretty much 
wiped out all the first night western direction contacts.  The 2nd night we 
used a work around noise cancelling configuration which helped a lot, but still 
kept us from a number of contacts and multipliers.

To set the stage, here are the factors involved.  1.  We have never had any 
significant noise on the Beverages over the past 10 years.  2.  The noise was 
BIG, and Broad band.  3.  It was the strongest on the JA Beverages, which from 
our station location is ~315 degrees.  4.  From the Beverage farm it is four 
(4) miles to the nearest power lines in the JA direction.  5.  I retired in 
January 2009 after 40 years of service at the local power company.  I know the 
circuits and all of the things to look for that might cause RF interference

N5BG and I spent some time the week after the contest, searching for the 
general source of the noise generator.  This past Tuesday Larry and I spent a 
couple of hours narrowing down the area.

I hooked up the K-3 to a VHF mag mount antenna and set it at 1.810 mHz AM.  We 
also had the AM broadcast radio set to 1710 kHz and the Yaesu FT-8800 dual band 
mobile set on 123.5 mHz AM aircraft band on the VHF side.  The intent here was 
not to be super sensitive.  We knew that when we got close to the source, that 
these radio setups would give us a definitive indication of our proximity to 
the noise generator.

With the S meter on the K-3 we were able to narrow the area down to one 
particular 3 phase lateral line on the a distribution circuit headed away from 
our area.  This circuit originates at the a substation about 5 miles from our 
location, goes north across the river, and then down the valley northwesterly 
for about 15 miles.  This location is about 3 miles from where we had 
previously thought the strongest noise was located, just from listening on the 
AM broadcast radio.  All of this area is in the direction of JA from our 
station location.

The S meter on the K-3 did its job.  With one trip down the valley it was 
determined that the strongest signal was closer towards our area and the 
substation than previously suspected.  

The S Meter on the FT-8800 confirmed we were near the source, because it 
actually came up and registered 2 segments when we were right under the line as 
it crossed the highway we were traveling.  It had never registered anywhere 
before, even though we could hear the noise quite often, and strong, in the 
aircraft band.

We inspected the poles on the lateral line and zeroed in on the last pole.  It 
has mounted on it a three phase transformer cluster for powering an irrigation 
pump.  In daylight I saw a suspect pole ground wire in close proximity to one 
of the two steel X-arm braces supporting the top two crossarms where the lines 
are dead ended.

This still didn't compute as the noise is so broad banded, and so strong over 
such a wide area, that I didn't think it could be generated by a simple 
hardware/ground wire situation.

It was just at sundown, and we both agreed that if there was an arc of the 
magnitude I expected, we could see it after dark.  We returned to the site at 
near dark and sure enough, it was quickly spotted by Larry while I was trying 
to listen for an arcing sound.

The hot line clamp which connects the lead from the top of the lightning 
arrester/cutout combo to one of the phase conductors was arcing.  It was VERY 
visible.  The irrigation pump was not operating, and probably hasn't since last 
fall some time.  However, the excitation current required for energizing the 
primary coil and core of the transformer is just enough to create a constant 
arc at 7.2 kV.

It makes sense now.  The arc is on a primary phase line, which in turn is VERY 
long antenna.  You just have to LOVE those spark gap transmitters.  This one is 
probably in the nanoWatts of PO, but the ERP is a whole lot more.  So, with the 
lengths of multiple lateral taps and the main circuit added together, there are 
perhaps 40 miles of antenna wire attached directly to the transmitter.

I have a jpeg shot off Google Earth which shows the relationship of Larry's 
place, the Beverage farm and the noise source location.  It is 6.5 miles at 300 
degrees from the Bevs to the noise source.  

The two JA Bevs, at 315 degrees, always had the strongest noise signal level 
(about S-5 average).  They consistenly told us the noise was in that direction. 
 I will send the jpeg shot to anyone who contacts me directly.

We prepared a letter describing the problem, suspect location and equipment.  
Larry submitted the letter to the power company people this morning.  

In less than 3 hours, the BIG NOISE went away.  The power company line crew 
replaced the hot line clamp, and all is well on the N5BG/NI5T Beverages.  This 
morning the noise was an S-6 level on Topband in the AM mode.  Now the level is 
background hiss.

In most cases if the amateur will search out the probable noise source and 
present it to the power company operations people, they will clean it up.  Most 
small, rural power company's do not have the in-house expertise, nor the 
equipment, to search for and find an RF interference problem.

Your mileage may vary, but it works for us.  CU all in CQ 160 SSB next week.

73 de Milt, N5IA  