[TowerTalk] Re: getting coax into shack thru wall

To: <towertalk@contesting.com>
Subject: [TowerTalk] Re: getting coax into shack thru wall
From: w8ji.tom@MCIONE.com (Tom Rauch)
Date: Fri, 29 May 1998 08:34:59 +0000
To: <towertalk@contesting.com>
> Date:          Thu, 28 May 1998 22:42:25 -0400 (EDT)
> From:          K7LXC@aol.com

Hi Steve,

>        " A nice low impedance path from the tower to the house" is a good
> start. Yes, it's not a 'ground system' but it's something that needs to be
> done.

You are welcome to do that at your house, but I won't do that as a 
"rule" at my house or at most of the commercial installations I 
oversee.

My closest tower is two feet from the house, and 60 feet tall. It 
is intentionally located near and bonded to the service entrance of 
power and telco lines, and has a driven rod and a small radial ground 
system. It contains TV antennas and a two meter antenna, and all 
cables enter with the telco and power cables, and share common 
grounds just outside the house.

My next closest tower is 250 feet from the house, and 200 feet tall. 
It is grounded by many thousands of feet of radials covering a ten 
acre pasture. That radial field cuts off before reaching the power 
line ground and house.

At my "last line of defense" at the edge of the pasture, I have 
lightning retarding chokes both before and after a separate 
driven rod independent ground. When I know of a storm, or when I go 
away, I pull the plugs on ALL the cables at that point and pull 
them back several feet.  

The last thing in the world I want is to bring any direct strikes 
that might elevate the earth around the tower into the house, where 
the current might cause problems. I want to minimize coupling between 
the tower and tower ground and the house and house ground, while 
letting EVERYTHING in the house rise together and everything at the 
tower do the same. 

>What a 'lightning protection system' should do is have everything 
>bonded
> together to minimize potential differences. It's these potential differences
> that cause the arcing and assorted damage to equipment.

That's true IN the house, or ON the tower, but you certainly don't 
need to make the house ground follow the tower ground if you can 
avoid it. If the tower is right against the house, the best idea is 
to bring grounds and cables all up together with minimal potential 
difference. If the tower is remote from the house, keep the grounds 
isolated but STILL use the common point method at each end of the 
system.

If the distance is greater, the problem becomes one of  isolated 
systems. Keep them that way if possible.

73, Tom W8JI
w8ji.tom@MCIONE.com

--
FAQ on WWW:               http://www.contesting.com/towertalkfaq.html
Submissions:              towertalk@contesting.com
Administrative requests:  towertalk-REQUEST@contesting.com
Problems:                 owner-towertalk@contesting.com
Search:                   http://www.contesting.com/km9p/search.htm

<Prev in Thread] Current Thread [Next in Thread>