[TowerTalk] Re: Lightning ground "Holy Wars"

To: <towertalk@contesting.com>
Subject: [TowerTalk] Re: Lightning ground "Holy Wars"
From: DAVED@ctilidar.com (Dave D'Epagnier)
Date: Mon, 1 Jun 1998 08:42:49 -0600
> ----------
> From:         Tom Rauch
> 
> 
> So a 1" wide strip has about the same inductance as a 1" wide round 
> tube, but with the same amount of material a flat strip has 
> less inductance because it can be made wider......
> By the way Tom, if you play with these formulas, the units are MKS,
> the inductance is in nH, I left a paranthesis out of the ribbon
> equation (tough to write equations here), and the wire equation is for
> solid wire, not tubing. The main point is that copper strip like the
> stuff you can get from Polyphaser (1.5"wide by 0.015" thick) is a lot
> lower inductance than the standard "wimpy" AWG#2 wire used for
> grounding, and a heck of a lot more flexible  than copper pipe (and
> more expensive than either!).
> 
> -- Dave
> 
>  
>       The reference can be derived from data in Magraw Hill
> > Electronics Engineers' Handbook.
> 
> Is that the one by Fink? 
yep

> 73, Tom W8JI
> w8ji.tom@MCIONE.com
> 
> 

--