At 01:43 PM 4/30/2004 -0400, K8fu@aol.com wrote:
Well the unanimous opinion was that horizontal installation of ground rod is
right up there with trying to get pet rocks to generate offspring.


Except that the regulatory agencies, who do actually analyze this stuff, think that horizontal ground rods are just fine.

For instance, page 131 of IEEE Std-142(1991) "IEEE Recommended Practice for Grounding of Industrial and Commercial Power Systems" has a table showing ground resistances for a variety of configurations, including "buried horizontal wire". Later, on pages 133-135, it discusses the advantanges of horizontal cable grounds, particularly where the soil is hard and/or of low conductivity. Mention is made that several short horizontal conductors may be better than a single deep rod because the inductance is lower.

NBS (now NIST) did tests which indicated that the resistance decreased only 5% when changing burial depth of horizontal rods and strips from 18 inches to 36 inches.

There are some recommendations as to depth of burial in places where it freezes.

Consider that UFER ground ("Concrete Encased Electrode) is considered fine, and has almost no vertical penetration.


Jim, W6RMK


_______________________________________________

See: http://www.mscomputer.com for "Self Supporting Towers", "Wireless Weather Stations", and lot's more. Call Toll Free, 1-800-333-9041 with any questions and ask for Sherman, W2FLA.

_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>