One other thing that just occurred to me. The "code" rules (for UFER and
other) are for a electrical safety ground, not necessarily for lightning
protection, which has a whole other set of aspects, not the least of which
is that lightning isn't 50 or 60 Hz.
As it happens, the original work by Herbert Ufer was for lightning
protection grounds, but that doesn't mean that the NEC required 20 ft of
conductor is appropriate for that application.
Jim