On Wed, 16 Jun 2010 14:27:25 -0700 (PDT), Tom Anderson wrote:

>Most grounding books and articles suggest

Both building codes and the laws of physics REQUIRE that connection, 
they do not SUGGEST it. :)  

It's unfortunate that your power and your ham station are on opposite 
sides of the house, but this condition is quite common. The connection 
must still be made, it must be as short as possible, and it must be 
robust. 

I've had that condition in two very different QTHs. A good solution is 
to run both a bond THROUGH the house (shorter), and AROUND the house 
at ground level. What I did was to drive several ground rods at the 
power service, bond them to the power system, run a #6 around the 
perimeter to the shack, drive 3 rods around the perimeter and tied 
them to the #6, drove three more rods at the shack, bonded those to 
the coax entry panel. The coax entry panel is bonded to the equipment 
on the operating bench. I have steel conduit (thinwall, also known as 
EMT) between the power panel and the shack outlets, so that conduit is 
also bonded to the coax entry panel, which is bonded to the ground 
rods and the gear on the operating bench.  

73, Jim Brown K9YC