"Regular" rebar vs weldable rebar. You don't weld regular rebar because of strength issues. With regular rebar you wouldn't weld anywhere strength is an issue due to embrittlement etc. However, welding something onto the end of a piece of rebar which is not going to be mechanically challenged at the weld should not be a problem.

For example: You want to attach a ground wire to the end of a piece of rebar. You can weld a nut to the rebar and then use a bolt to attach an electrical terminal to the end of the rebar. The nut (and bolt) can be stainless steel if you prefer. You should waterproof the above connection. Wrap with good tape and cover with silicon rubber or use your favorite weatherproofing process. A good electrical compound such as no-alox or equivalent can also be used in addition to the weatherproofing..

Cad-welding to the end of a piece of rebar that is not going to be heavily stressed mechanically should not pose a problem (issue for the younger set.)

Patrick        NJ5G


On 7/15/2016 11:03 AM, Paul Christensen wrote:
"I thought that one is NOT supposed to ever weld to the rebar, unless the
rebar is spec'd for welding, which most are not"

No idea, but Erico sells many forms of Cadweld shots that are designed to
bond coper wire with rebar.  Anyone know the answer?  Is there a special
form of rebar that can only be used with an exothermic weld?

Paul, W9AC

-----Original Message-----
From: TowerTalk [mailto:towertalk-bounces@contesting.com] On Behalf Of Dick
Blumenstein
Sent: Friday, July 15, 2016 11:59 AM
To: towertalk@contesting.com
Subject: Re: [TowerTalk] Ufer Grounding

Hi Paul-

I thought that one is NOT supposed to ever weld to the rebar, unless the
rebar is spec'd for welding, which most are not; that all grounding wire
should be clamped to the rebar and then when the wire leaves the area of the
tower base, you should/could cad weld it to the ground rod system.
Am I wrong here? (I'm about to build a concrete tower base with a 5' x 5' x
8' deep hole and a lot of rebar).

Dick, K0CAT

============================


Paul Christensen wrote on 7/14/2016 10:48 PM:
It's looking more probable that the remote Internet site built last
year by N4CC and myself will require a complete move about a half-mile
down the road.  Assuming this is the case, I want to pay particular
attention this time to Ufer grounding of the two tower bases.  These
are large Pirod self-supporting towers with substantial concrete
piers.  The relevant portion of Motorola's R56 standard is copied and
pasted below.  The soil in this area is very sandy and at the current
site, we ended up having to drive down a total of four 24 ft. rods to get
adequately low earthing resistance.
That was a rough day of work even with a hammer drill.

My thought is to "spiral wind" solid #2 AWG wire, beginning the bottom
rebar layer.  Cadweld it at the start point, and then periodically
Cadweld at random points where the wire crosses other rebar sections.
The wire would exit at the top of the pier using a small-diameter PVC
pipe as shown in one of the R56 diagrams.  As the wire nears the top,
possibly it could branch out into two additional directions for
bonding to the tower base and perimeter ring.

Any issues with this plan?

Paul, W9AC

Motorola R56 Ufer Guidelines:

. Concrete-encased electrodes shall be encased by at least 51 mm (2
in.) of concrete, located within and near the bottom of a concrete
foundation or footing that is in direct contact with the earth.

. Concrete-encased electrodes shall be at least 6.1 m (20 ft.) of bare
copper conductor not smaller than 25 mm2 csa (#4 AWG) or at least 6.1
m (20 ft.) of one or more bare or zinc galvanized or other conductive
coated steel reinforcing bars or rods at least 12.7 mm (0.5 in.) in
diameter.

. Concrete-encased electrodes shall be bonded to any other grounding
electrode system at the site.
See "Common Grounding (Earthing)" on page 4-5.

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>