Merit W6NQ says:
>I wonder if it might be best to reverse pri & sec to the mains.
>(LV to the secondary side.)
>You are only going to need a few volts from the variac with the
>ammeter shorting the opposite winding.
In that case, the rms current measured on the amp meter must be multiplied
by the xfmr ratio
eg a 220 to 2200 volt xfmr and you want to test at 1 amp in the HV winding:
then if reversed, you need 10amps in the 220 volt winding and through the
amp meter
>(I blew a meter once doing this test when I was careless.)