Amps
[Top] [All Lists]

Re: [Amps] HV transformers I want to series primary andparallelsecondary

To: "Larry Carman" <lncarman@swbell.net>, <amps@contesting.com>
Subject: Re: [Amps] HV transformers I want to series primary andparallelsecondary
From: "Tom W8JI" <w8ji@w8ji.com>
Date: Fri, 18 Aug 2006 18:51:37 -0400
List-post: <mailto:amps@contesting.com>
> If I place the 110 primaries in series and also series the 
> secondary using
> the common connection on the secondary as a CT, would 
> equalizing the
> currents in the transformers be necessary if the secondary 
> voltagse of the
> transformers differed more than say 25 volts or so.

When using a grounded CT, you give up supply regulation 
compared to paralleling the windings. So I would not use 
that method, it wastes transformer copper since for 50% of 
the total on time one winding is doing nothing at all.

Parallel with a bridge is the only way to go if you want 
good regulation.

If you series either primary or secondary pair or series 
both primary and secondary pairs, you  don't need a separate 
bridge. It does no good at all.

> Another question: If the secondary voltages differed more 
> than 30 or 40
> volts and I used separate bridges, how much of a potential 
> problem would
> that be?

Not much. The ESR of the transformer, which includes primary 
and secondary resistances and core losses, and is always 
more than the dc resistance of the secondary (so you could 
use that as a conservative easy to measure value). This 
resistance equalizes currents. If the voltage drop from no 
load to full load was 300 volts dc and there was only 30 
volts open circuit voltage difference, you would have less 
than a few percent difference in transformer power loading 
when using separate bridges.

The difference in no load voltages would have to be a large 
value compared to the dc voltage drop under full load for 
the transformers to be unbalanced when using separate 
bridges. I think you are worrying about nothing. The only 
condition that is a problem when using similar transformers 
is when both the primary and the secondarys are paralleled.

73 Tom 


_______________________________________________
Amps mailing list
Amps@contesting.com
http://lists.contesting.com/mailman/listinfo/amps