[Amps] Re: Step-start calculation
jeff millar
wa1hco at adelphia.net
Sat Nov 20 12:04:32 EST 2004
PSU designer (http://www.duncanamps.com/psud2/download.html) can do this
calculation and I've got it running here. The model needs some values
for various parameters. Here's some results for some sample HVPS with
zero voltage switched
Case 1:
Transformer
1500V secondary, 10 Ohms
240V primary, 0.1 Ohms
Full wave doubler
40 uF caps (2)
Results
4K load impedance
Output ripples from about 3900 to 3700 (~5%)
Peak current at turn on 27 Amps
Peak current on each line cycle 9 Amps
Case 2:
Transformer
2600V seconday, 10 Ohms
240V primary, 0.1 Ohms
Full Wave Bridge
40 uF cap
Results
4K load resistance
Output ripples from about 3500 to 3300 (
Peak current at turn on 42 Amps
Peak current on each line cycle 6 Amps
Adjusting parameters and generally looking at result shows
Magnitude of turn on current surge mostly depends on capacitance
Transformer resistance has little effect (surprise!, change values
about 20%)
Peak current at turn on of 5-10 times cycle to cycle peak with
enough capacitance to limit ripple to 5%
Conclusion...
Zero voltage turn on works
Keep the capacitance low (good idea anyway to limit flash over damage
If anyone wants to run the model with different values just send me an
email. Or if you get some interesting results, please post them.
jeff, wa1hco
Roy Koeppe wrote:
>I don't like to think about it. I gives me a headache.
>
>73, Roy K6XK
>
>
> "...What would be a suitable
> value of step-start R to limit the inrush current to 50A-rms?..."
>
>
> In this practical & real world, it would be 4.6 ohms.
>
>Congrats, Roy. The closest value in my junk box was 5.6½s.
>