In a message dated 11/15/2005 11:25:17 PM Eastern Standard Time,
garyschafer at comcast.net writes:
It could be due to leakage to earth or it could be a path through your body
to earth if you come in contact with the hot lead. Or it could be if the hot
comes in contact with the ground lead.
A GFI will function perfectly well with no safety ground involved.
73
Gary K4FMX
This is exactly true. A GFI only sees that the same amount of current
returns on the nuetral than is going out on the hot. It the difference is more
than 3-6 milliamps the GFI shuts off. The assumption is that the missing
current can be going through YOU!