[Amps] MOV Sizing

Tom W8JI w8ji at w8ji.com
Sat Mar 3 18:05:13 EST 2007


MOV's should never tie to the safety ground lead or any 
ground lead outside of an entrance panel. They can have very 
large fault currents and, if sized to close to the power 
line voltage, can go into thermal runaway.

They can tie back to a suitably sized neutral lead, but we 
all know the neutral cannot be grounded at the equipment.

Since the clamping voltage is pretty high anyway, you might 
as well size for some margin. I'd use MOV's rated at 140-150 
volts continuous AC if I was sure the line would never go 
over 120.... if I used MOV's.

73 Tom 




More information about the Amps mailing list