[Amps] 240V Outlet
Martin A Flynn
maflynn at att.net
Sun Aug 9 18:00:01 PDT 2009
Martin Wrote:
>> Paul,
>> The breaker and device are the same rating. My comment was to state
>> that his recommendation was to make the conductors and ground one wire
>> gauge larger then NFPA 70 states it should be.
>>
>> Martin
> That only makes sense if the I*R drop is excessive. Since the Invader
> 2000 is only going to draw about half the ratings of #12 wire, then
> going to #10 makes little sense on a basement long run. Going to #10
> requires all different plugs and outlets and the cost about goes thru
> the roof compared to a 20A feed.
The FPN notes in NFPA 70 (which is not part of the actual document)
suggests no more then a 5% total drop between feeder and branch
circuits. Here's the quote: (fair use excerpt)
Art 210-19(A)(1), FPN No. 4: "Conductors for branch circuits as defined
in Article 100, sized to prevent a voltage drop exceeding 3 percent at
the farthest outlet of power, heating, and lighting loads, or
combinations of such loads, and where the maximum voltage drop on both
feeders and branch circuits to the farthest outlet does not exceed 5
percent, provide reasonable efficiency of operation.
In the original case I commented on the run is ~50 feet, straight line
distance. Service is 120/208 3 phase A licensed electrician made the
calculations, presented them to the electrical inspector, and both
agreed that the oversize wire was appropriate.
I did the same at home. The difference in cost between #12 THHN and #10
THHN was negligible. I used Square D breakers and Hubbell connectors.
Since the wire clamp range on a Hubbell HBL2410 - 20 Amp twist lock is
18-10 AWG, and the 20 amp 2 pole QOB Square D breaker is 14-8 AWG, it
fit together fine with no difference in cost other then the wire.
Martin
More information about the Amps
mailing list