[Amps] 240V Outlet

Scott McGrath mcgrath at fas.harvard.edu
Wed Aug 12 17:28:00 PDT 2009


One fact lost in the 15 vs 20 amp outlet discussion is the NEC requires you to derate any circuit to 80pct of its full load capacity for loads which are steady state.   So a 20A circuit is allowed only to have 16A drawn.   In data centers we have to abide by this rule

-----Original Message-----

From:  "jimsmitheguard-a at yahoo.com" <jimsmitheguard-a at yahoo.com>
Subj:  Re: [Amps] 240V Outlet
Date:  Wed Aug 12, 2009 20:00
Size:  791 bytes
To:  "amps at contesting.com" <amps at contesting.com>

You are more likely to find 20 amp plugs on commercial equipment. 
  
So I wonder why anyone wants to install all 20 amp receptacles? 
  
Jim Smith, EE 
KQ6UV 
 
--- On Wed, 8/12/09, Gudguyham at aol.com <Gudguyham at aol.com> wrote: 
 
 
From: Gudguyham at aol.com <Gudguyham at aol.com> 
Subject: Re: [Amps] 240V Outlet 
To: jimsmitheguard-a at yahoo.com, amps at contesting.com, jim at audiosystemsgroup.com 
Date: Wednesday, August 12, 2009, 4:45 AM 
 
 
 
  
The only time I have seen a 20A 120v plug on anything was when I saw a commercial 120v floor sander, don't think I have ever seen an appliance you can buy in any home goods store with a 120v 20A plug. 
 
 
 