On 4/5/2011 8:57 AM, Gary Schafer wrote:
> Under today's NEC rules you always need a ground rod at the remote panel if
> the remote panel is not in the same building as the main panel. And they
> want a separate ground and separate neutral wire run from the main panel.
> Ground and neutral remain separate in the remote panel.
Remember that this is what I described as Method #2. Method #1 allows
bonding neutral in the second building with no ground between buildings.
73, Jim K9YC