[Amps] 4 wire 240VAC service? What to do now?

Jim Brown jim at audiosystemsgroup.com
Tue Apr 5 10:05:09 PDT 2011


On 4/5/2011 8:57 AM, Gary Schafer wrote:
> Under today's NEC rules you always need a ground rod at the remote panel if
> the remote panel is not in the same building as the main panel. And they
> want a separate ground and separate neutral wire run from the main panel.
> Ground and neutral remain separate in the remote panel.

Remember that this is what I described as Method #2.  Method #1 allows 
bonding neutral in the second building with no ground between buildings.

73, Jim K9YC


More information about the Amps mailing list