Jim Barber N7CXI wrote:
> If you were looking at a Dahl plate transformer removed from a BC
> transmitter that had a center-tapped secondary, would you bet that the
> insulation would be good enough to use the transformer with a bridge
> instead of a full-wave rectifier, or would you assume that it isn't for
> safety's sake?
Get the secondary winding Hi-Potted at 10 or 15 kV, don't guess. (hV tested)
--
Ron KA4INM - Ifen my mother in law were to boil water
it would taste funny ... Earl Pitts 9-1-11