[Amps] The Pin One Problem - Common Impedance Coupling

Jim Brown jim at audiosystemsgroup.com
Fri Jun 7 18:48:33 EDT 2013


On 6/7/2013 12:54 PM, Roger Parsons wrote:
> I think that a technically correct generic name for the 'Pin 1 Problem' would be unwanted 'Common Impedance Coupling', and a bit of a search shows that this term has been quite frequently used.

No, it is NOT the correct description.

Joe hit the nail on the head, and Paul got a lot of it right.

Old time broadcasters who "never saw these problems in big consoles" 
were almost certainly working on gear built in the old days, when a jack 
was screwed down to the chassis, and the shield went straight to the 
chassis.  Pin One Problems began to abound when mfg got too efficient 
for its own good, with connectors that mounted to the circuit board, but 
forgot that shields had to make contact with the chassis.

Now I'm going to really arouse folks -- there is no such thing as a 
"ground loop!"  When power line "buzz" couples into unbalanced wiring, 
it is because the chassis of two pieces of equipment being connected are 
at different potentials, and that potential difference is added to the 
signal. The fundamental cause of the potential difference is nothing 
more or less than LEAKAGE current from the AC power system.  The path 
for this current is capacitance between the "high" side of the AC power 
line and the chassis, which must, by law, be connected to the "green 
wire" of the AC line, that current returns to its source (the power 
system) via the green wire, and the current produces IR drop in the 
green wire. That IR drop is what we hear.

The leakage current consists primarily of the HARMONICS of 60 Hz, which 
is why we hear "buzz" rather than "hum" (pure 60 Hz). Why harmonics?  
Because nearly all equipment we connect to the power line as a load has 
a capacitor-input power supply, which causes current to flow in 
relatively short pulses at the top and bottom of each cycle, which in 
turn makes the current rich in harmonics.

As if that weren't enough, in three-phase systems, "triplen" harmonics 
(any harmonic number divisible by  three) will ADD both in the neutral 
and in the ground. Few of us have 3-phse in our homes, but the vast 
majority of homes are fed by 3-phase distribution systems. As a result, 
almost all of us will see a lot of triplen harmonics if we do an 
spectrum display of the power line, and of the voltage between one 
chassis and another of equipment plugged into different outlets.

So what we incorrectly call a "ground loop" and do stupid things to 
avoid, is really AC leakage current, and the cure is VERY simple.

1) Minimize the voltage difference between one chassis and another by 
getting power for everything that will be interconnected from the same 
AC outlet, or from outlets that share the same green wire, or from 
outlets that are bonded together by short fat copper.

2) Bond with short, fat copper from chassis to chassis of every piece of 
gear that has an unbalanced connection.

#1 takes the IR drop of the long "green wire" from the outlet to the 
panel out of the picture, so the remaining IR drop is only the short 
(typically 6 ft) line cord.  #2 helps two ways. First, shorts out the 
remaining potential difference by brute force.  Second, it diverts that 
leakage current (and most of the RF that might be picked up on a short 
cable) to the chassis, so it also cures any Pin One Problems that might 
be present.

In the tutorials I do for pro audio/video trade shows, I call this 
technique "local bonding," emphasizing the fact that it only works where 
cable lengths are short enough that the resistance of the bonding 
conductors is low.

As I see it, there is one, and only one, good time to use the word 
"loop" in a discussion of noise coupling, and that is when the coupling 
mechanism is the MAGNETIC field.  With all magnetic coupling, the 
strength of both the field and the sensitivity of a system to a magnetic 
field is the LOOP AREA of the coupling path. In our stations, we 
commonly see magnetic coupling in three situations.

1) Leakage flux from big power transformers close to our equipment 
and/or its wiring.

2) Wiring errors in the power system that establish a magnetic field. 
Perhaps a neutral is bonded to the green wire at more than one point, or 
a load is connected between  "hot" and "green," or an outlet is mis-wired.

3) We feed a long wire antenna that ends in the shack, and thanks to the 
length of the antenna, there's a current peak near our equipment.  That 
current produces a strong magnetic field.  As has been observed, a cable 
shield provides NO magnetic shielding at power frequencies, and TWISTED 
PAIR is VERY effective at rejecting magnetic fields.

73, Jim K9YC


More information about the Amps mailing list