On 2/4/2020 9:43 PM, Mark Schoonover wrote:
> Actually reviewing the wiring diagram for a standard breaker box and  the
> ground wire isn't  attached to a circuit breaker at all.

Right. The green wire goes to the panel's ground bus, which is bonded to 
the panel enclosure. Neutral is bonded to the equipment enclosure where 
power enters the premises. Neutral and green are bonded at that point, 
and ONLY that point.

The function of the "green wire" is to provide a low impedance path to 
blow the fuse or breaker in the event of a fault that causes the chassis 
to be hot.

73, Jim K9YC