[Amps] Alpha 87A Power Supply Question

Jeff DePolo jd0 at broadsci.com
Tue May 4 21:52:26 EDT 2021


Agree with everything you said Jim, with one exception:
 
> The only condition in which a Green wire is permitted to carry load
> current or is permitted to be bonded to neutral is a "grandfathered"
> installation of an appliance that was done before the Code changed to
> prohibit it.

Not quite right.  In those few exceptions, you are permitted to bond the
NEUTRAL to the frame.  You are not permitted to use an EGC as a
current-carrying conductor (i.e. as a neutral) for the 120V loads.  

				--- Jeff WN3A



-- 