[Amps] What to do about 'Neutral' in HB amp?

Jim jimw7ry at gmail.com
Wed Dec 28 18:03:41 EST 2022


See my comments below.

Thanks, 73, Jim W7RY
A certified Motorola R56 Inspector.

On 12/28/2022 4:10 PM, n4is at comcast.net wrote:
> That is a catch 22.
> The NEC for residence is not the same for a Radio Station, and  R56 -
> Standards and Guidelines for Communication Sites. However we have a
> residence and a Radio Station on the same lot.
> Proper ground system for both requirements are very expensive and ignored by
> most of ham stations I visited on my previous antenna business.
> It is not what to do with the neutral only on the 240Vac amplifier, it is
> the RF ground, AC ground and neutral at the residence and at the station.
> The Towers ground has another complication, lighting and RF ground plane.
> Besides the NEC code and R46. The ground for lighting requires a 00 cable


No.. Just #2 tin plated (or larger) to the external grounding electrode 
system. Most systems use several #2 AWG tin plated conductors to the 
external grounding (bonding) electrode system.

> from the leg of the tower to several ground rod. The ground for RF require
> radials, The ground for NEC requires only one point of connection with the
> AC entrance ground, where the NEUTRAL is connect, and ALL the NEUTRAL must
> be connected to only that single point, next to the AC meter, or AC
> entrance. There is one ground rod there for that.

> Also any rotor cable, control cable and any coaxial cable from the tower
> must be properly grounded in several points.
> All this complexity goes to the station with cables coming from the tower
> into the Amplifier and cables from the amplifier to the AC wire of the house
> including the neutral !
> The solution at my station to comply and be safe with all standards
> requirements was to use a 240Vav  3KW medical isolation transformer for the
> 110AC at the station and the center to the RF ground outside the house. The
> same 240Vac line from the Amplifier and the isolation transformer does not
> use the neutral from the house wiring, but goes to the outside RF ground
> that has a 00 cable and several ground rods with only one connection to the
> Neutral at the AC entrance, the same as the AC outlet on the wall from the
> house wiring. All my cables and from the tower are grounded outside the
> house, inside a large steel galvanized box, grounded on that 00 cable.


Kinda hard to follow.. But what you are explaining is separately derived 
electrical system. Which must have a ground/neutral bond back to the 
external grounding (bonding) electrode system.

We often used isolation transformers when the run between the main 
building electrical system was over 100 feet. Really helps in stopping 
surges events from getting to the originating building.

> So, the neutral is connected as NEC requires, it is safe and comply with
> r56. The 240 Vac to the station has a larger AC common mode filter with the
> house neutral at the input and only to phases out for the 240 Vac, for the
> amplifier and the isolation transformer, the center of the secondary 110+100
> is the neutral of the station, connected to the house neutral in only one
> point at the entrance of the house. No neutral loop ground!!


You mean ground. Not neutral?

>
> If you don't follow all requirements, your station will suffer severer
> damage with any lighting event and the way you connect the neutral to your
> amplifier will means nothing.  Be safe.
>
> 73's
> JC
> N4IS
>
> _______________________________________________
> Amps mailing list
> Amps at contesting.com
> http://lists.contesting.com/mailman/listinfo/amps


More information about the Amps mailing list