On 12/30/2022 11:41 AM, donroden at hiwaay.net wrote:
> Do you really need the fourth wire if there is a ground / case lug on
> the back of the amp tied to your station ground ? W4DNR
YES! Code requires that the green wire run with the current-carrying
conductors. We CAN do that with a conductor from the outlet's green wire
to the amp, running with the existing line cord.
73, Jim K9YC