Now that you say it that way I start suspecting the auto transformer.
Assuming nothing is miswired (and I have to rewire anyway to route the
wires nicely - currently it's only a "working" setup) it is the only place
that is not fully isolated.
As expected in an auto transformer the neutral just passes through to the
rectifier then minus of the rectifier is connected to the ground/case.
I had RCD trigger before I fitted the auto transformer, but only once, so
it may have been a temporary short.
This is not ideal. I have to use it as auto transformer as all normal
transformers I have, have far too high voltages. (for example a 230 to
415,after rectifying it results in 580V. That turns into a pot of heat if
it has to be shunt stabilised to 350V. It's very hard to find 230-300V
transformer.
The "auto transformer" is a normal 240-2*36V toroid but connected like this:
Low side of 240V is neutral that passes through, high side is connected to
live 240V, then low side of the first 36V is connected to that, high side
is connected with low side of the other 36V. Finally the remaining high
side has approximately 300V AC and goes to the rectifier. I think it is the
most likely culprit.
73,
Luk - SP4IT
On Fri, 29 Nov 2024, 20:20 Michael Tope, <W4EF at dellroy.com> wrote:
> Luk,
>
> At least for amplifiers I've seen here in North America, the isolation
> between the chassis metal and the power mains neutral typically come
> from the HV transformer (and any additional transformers that are used
> for producing things like filament voltage, control voltages, etc). Do
> you have any connections between the lines on the primary side of your
> transformers and the grounding conductor? In other words, I am trying to
> understand why you need an isolation transformer to prevent RCD/GFCI
> trip when the transformers in the amplifier should provide that function?
>
> 73, Mike W4EF
>
> On 11/28/2024 3:52 PM, Lukasz wrote:
> > Hi Jim,
> >
> > It is similar here in the EU as far as I know.
> >
> > A typical way devices, are constructed here is that the ground (including
> > the case if made of metal) is not used as a normal current path in the
> > device. One sees current flow on that ground only in a fault scenario.
> >
> > This means RCD/GFCI protections can work as when it see any discrepancy
> in
> > the live/neutral current balance it shuts the circuit down.
> >
> > These rules normally mean one always has a return current path within the
> > device that is separate from ground (neutral, DC minus etc), but this is
> > difficult when the amplifier is entirely made of metal and one would
> prefer
> > to have a current return plane (for example the floor if the case) rather
> > than route separate connections for DC minus and RF ground.
> >
> > This is not how OLD devices were made. I have a couple of old lathes and
> > mills that do use the steel frame as neutral/ground(one connector called
> > PEN) . This is how, it seems, all tube amps are built I saw pictures so
> > far.
> >
> > So my question is, if one wants to build a tube amp in a modern way.
> > Properly grounded, is building a case within a case and electrically
> > isolating the two the only way? Or has anyone managed to build a tube
> > amplifier in a single grounded steel case. That works normally within the
> > usual electrical systems (with gfci/rcd protected circuits). If so,
> please
> > describe how are all the current return paths done.
> >
> > 73,
> > Luk, SP4IT
> >
> > On Wed, 27 Nov 2024, 23:05 Jim Brown, <jim at audiosystemsgroup.com> wrote:
> >
> >> Hi Lukasz,
> >>
> >> In North America, the protective earth MUST be carried in the same cable
> >> with the current-carrying conductors, and MUST be bonded to the chassis
> >> at the point where that cable enters. I'd be surprised if it's different
> >> in EU -- it must be done that way to be protective!
> >>
> >> There's another requirement in NA -- all grounds (earths) MUST be bonded
> >> together. Again, protective against both lightning and electrical shock.
> >> So when power goes through ANY transformer that's not part of equipment,
> >> protective earth MUST be carried from one side of the transformer to the
> >> other.
> >>
> >> I don't remember about EU, but I do remember that in the UK, no earth
> >> connection to the power system is permitted -- that happens only within
> >> the power distribution system.
> >>
> >> When thinking about this and antennas, remember that the earth is a big
> >> resistor, and parts of antennas like radial systems are NOT intended to
> >> couple to the earth, but rather to shield the EM field from the earth,
> >> and to provide a low resistance path for the antenna's return current.
> >> The only antennas that benefit from an earth connection are SOME
> >> receiving antennas, like Beverages and loops.
> >>
> >> 73, Jim K9YC
> >>
> >> On 11/26/2024 8:10 AM, Lukasz wrote:
> >>> Hi,
> >>>
> >>> Is there some way to build a tube amp in a metal case, using the case
> as
> >> RF
> >>> ground, and not have current flow out of the amp through the grounding
> >>> conductor? (other than isolating that ground from the case entirely,
> >> which
> >>> presents it's own problems - for example capacitive coupling to the
> >> case).
> >>> I'm currently experimenting with an amp and I have to power it via an
> >>> isolation transformer (the high voltage is 3 phase on its own circuit
> >> with
> >>> no GFCI temporarily) or my RCD will trigger.
> >>>
> >>> The high voltage power supply is an old military device that used its
> >>> chassis as ultimate DC ground (hv ground connects to it through a
> >>> overcurrent protection coil).
> >>>
> >>> Then I also used the chassis as ground for DC HV, screen and grid
> >> supplies.
> >>> This I could swap, but it's the RF ground (especially the Pi tank) I'm
> >>> concerned about.
> >>>
> >>> Is essentially isolating amp RF ground from the grounding conductor
> >>> (PEN/EGC or whatever it's called where you are) the only way?
> >>>
> >>> 73,
> >>> Łukasz, SP4IT
> >>> _______________________________________________
> >>> Amps mailing list
> >>> Amps at contesting.com
> >>> http://lists.contesting.com/mailman/listinfo/amps
> >>
> >> _______________________________________________
> >> Amps mailing list
> >> Amps at contesting.com
> >> http://lists.contesting.com/mailman/listinfo/amps
> >>
> > _______________________________________________
> > Amps mailing list
> > Amps at contesting.com
> > http://lists.contesting.com/mailman/listinfo/amps
>
>
> _______________________________________________
> Amps mailing list
> Amps at contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
>
More information about the Amps
mailing list