yes, donated.

Kim observed tat kohler for example rates generators at 300% for 10 sec.

I have requested info from the manufacturer so maybe.... we just need bigger service wires.

but this is intriguing.  big hv cap bank. that might be the best route if the generator cannot be overloaded.

I figure this overload might be 3-4 times each day?


On Wed, Sep 14, 2016 at 11:31 AM, Ron Rogers <ww8rr@charter.net> wrote:

Storage for AC ??  Auto batteries and some BIG commercial inverters (as used in solar installs) phased and paralleled ?

 

https://www.zoro.com/schneider-electric-inverter-2500w-150a-120240vac-rnw8652524/i/G6869457/

Won’t be cheap !

 

I take it there is no Aux DC input to this machine ?

 

Was this machine donated to the mission ?

 

Ron

WW8RR


From: Fourlanders [mailto:fourlanders-bounces@contesting.com] On Behalf Of Bill Pence
Sent: Wednesday, September 14, 2016 10:05 AM
To: Fourlanders
Subject: Re: [Fourlanders] engineering chalenge

 

I see I left off the 10kw gen is diesel.

 

On Wed, Sep 14, 2016 at 9:53 AM, Bill Pence <pence.bill@gmail.com> wrote:

missions clinic in Haiti tat a friend supports has:

 

10kw generator  (40A @ 240v)

 

new device x-ray machine with max 2.5 seconds 100A @240v

 

economical ways to supply this?

 

the generator is rated 10kw max, 9kw cont.

 

budget? low...

 

 

I've not added much detail. I am looking for storage ideas that are economical.

 

I am unsure of how many xrays would be done each day, but let's think on maybe 1-2 dozen...