[RFI] ISOBAR
Pete Smith N4ZR
n4zr at contesting.com
Wed Sep 19 06:43:16 EDT 2012
Hi Dale - Yes, I do disconnect at the point of entry to the shack, and
no, there was no evidence of scorching on the roof.
I was in the shack when the hit occurred, and it was very loud and
seemingly close - I'm not sure but suspect that some share of the strike
current arced across the bulkhead connectors on my panel, something I
have seen before with nearby strikes. However, nothing was visibly
damaged.
Everything active on the tower - two rotators, an antenna relay box, and
a Stackmatch - was damaged, though not vaporized. I suppose this means
that the tower's grounding took much of the energy. I thought at the
time that the hit was on my F12 40m yagi, because one of its loading
wires was broken, but it could have been on the mast a couple of feet
above it. I bet it gave the long-time-resident wasps in the mast a
headache!
73, Pete N4ZR
The World Contest Station Database, at www.conteststations.com
The Reverse Beacon Network at http://reversebeacon.net, blog at reversebeacon.blogspot.com,
spots at telnet.reversebeacon.net, port 7000 and
arcluster.reversebeacon.net, port 7000
On 9/18/2012 10:15 PM, Dale Svetanoff wrote:
> Pete,
> Thanks for the detailed reply. Yes, given the second floor shack
> location (which I had in my younger days), I agree with your
> contention about disconnect being the most effective approach. You
> validate that concept by mentioning a direct hit. My one remaining
> question: Since your shack is second floor, I presume that you
> disconnect the cables on the inside of the entrance panel, thus
> isolating the equipment from the outside lines that could be exposed
> to a direct hit and/or coupled currents. That means the cables are
> still attached to the outside of the entrance panel and you mention
> that the wire grounding it runs along a first floor porch roof. Have
> you ever noticed any evidence of scorching to that roof after a hit?
> Again, thank you for sharing details with us on the reflector.
> 73,
> Dale Svetanoff, WA9ENA
> Sr EMC Engineer
> E-N-A Systems, LLC
> Specializing in shielding applications, system grounding, and
> lightning protection
>
> ----- Original Message -----
> *From:* Pete Smith N4ZR <mailto:n4zr at contesting.com>
> *To: *svetanoff at earthlink.net <mailto:svetanoff at earthlink.net>
> *Cc: *rfi at contesting.com <mailto:rfi at contesting.com>
> *Sent:* 9/18/2012 3:40:45
> *Subject:* Re: [RFI] ISOBAR
>
> Answers interspersed.
>
> 73, Pete N4ZR
> The World Contest Station Database, atwww.conteststations.com
> The Reverse Beacon Network athttp://reversebeacon.net, blog at reversebeacon.blogspot.com,
> spots at telnet.reversebeacon.net, port 7000 and
> arcluster.reversebeacon.net, port 7000
>
> On 9/18/2012 10:46 AM, Dale Svetanoff wrote:
>> Pete,
>>
>> Two questions: 1) That 40 feet of bare #2 wire between the entrance panel
>> and power line ground - I assume it is run outside, and if so, how many
>> ground rods are on it?
> My shack is on the second floor - the wire runs along a first
> floor porch roof and then down the side to the existing ground rod
> that also serves the main electrical panel.
>> 2) Does the wire provide all of the grounding for
>> the entrance panel, or do you have one or more ground rods tied to the
>> panel?
>
> See above
>> While I understand and agree with your comment about non-ideal
>> installations, I think the point has to be made that trying to accomplish
>> as good of an installation as possible should be a prime goal of every
>> radio installation design. The two most important factors, in ANY case,
>> are: A) Keep the lightning current on the outside of your
>> shack/house/vehicle; B) Design for as low an impedance as possible between
>> the entrance panel and earth ground and between tower (or antenna support)
>> and ground. Naturally, net Z will be the total of Xsub-L + wire resistance
>> + bonding resistance + earth coupling resistance. Net Z should be figured
>> for frequencies in the range of about 100 kHz to 10 MHz, the main spectral
>> distribution of lightning energy. (Yes, it extends upwards to nearly 100
>> MHz, but at greatly reduced energy levels.)
>
> My shack location virtually assures that I cannot achieve a
> good-enough installation so that I should count on it. My
> solution, which has worked so far (including a direct hit on the
> tower) is to disconnect everything at the entry panel.
>> The latter is essential during the strike because of the huge currents
>> during a strike. Since all of the station equipment is tied (bonded) to
>> the one ground system (or should be), the lower the net Z to ground means
>> the less voltage developed differentially between grounded connections and
>> power feeds, antenna inputs, and so forth. (This is in addition to the
>> common mode induced currents from a strike.) Keeping the lightning
>> current on the outside of the building is key to minimizing what I call the
>> "Kingsford Effect" (conversion of a building into a pile of charcoal) and
>> is usually handled well by a good entrance panel, well-grounded, and
>> equipped with protective devices for each and every I/O line used in the
>> station. I can personally vouch for the effectiveness of that approach.
>
> I contend that disconnecting the cables is probably as good as
> you're going to get in my situation.
>
More information about the RFI
mailing list