Four 8ft ground rods spaced further apart would be better.  Up to 16ft apart
max.  Bonded together underground as well.
Add a few more rods, and you could reach the AC panel's ground to bond it
all together.  Run at least #2 or better, or better yet 2" or 3" strap. for
the underground buss keeping any corner curves as wide as possible.  
Always meet local codes and NEC for minimum # of ground rods and bonding.
Add more as needed.

73, de ed -K0iL

-----Original Message-----
From: RFI [mailto:rfi-bounces at contesting.com] On Behalf Of Kenneth G. Gordon
Sent: Wednesday, October 05, 2016 1:28 PM
To: Bob K6UJ; rfi at contesting.com
Subject: Re: [RFI] Station ground - more

On 5 Oct 2016 at 11:17, Bob K6UJ wrote:

> What would you guys advise in my case ?
> The main panel is grounded as described to a ground rod.
> My ham station has a common bus that all the equipment ties into and 
> this ties into four 8 ft ground rods spaced 6 feet apart right outside 
> the shack.  As I understand it my station ground should tie into the 
> main panel ground.  But in my case, the main panel is on the opposite 
> side of the house and garage.  (about 60 feet away)  Should I run a 
> wire under the house and across the garage floor along the wall (the 
> garage has a concrete slab floor) to tie my station ground to the main 
> panel ground ?  (ouch)

"Ouch!" is right!

For one thing, the first thing that hit me was that "60 feet"which is
awfully close to a 1/4 wave on 80 meters. Potential problems there? I don't
know. I only suspect.

Is it possible for you to (yes) run say a #00 stranded copper wire from the
panel ground to your station ground, adding other ground rods at places in
between the ends to break up the distances?

Also, it seems to me that one ground rod at the panel is not really enough.
I used three here, but then again, ground conductivity in my area is VERY
poor.

Jim would know far more about this than I do, but if I were in your
position, I think I would try what I suggested above.

Ken W7EKB

---