> Re: the tower 350 ft from the house. I would bond the ground rods at the
> tower to the service entrance ground. I would bond the coax to the
> ground rods at the base of the tower, put a big ferrite choke on the
> coax at the base of the tower (between the shack and the ground point),
> and another before it comes into the shack. I would also have a bond
> between the shack and the service entrance. . I would also have
> Polyphasers on each coax at the shack to protect the front ends of the
> radios.
>
> What this does is start with everything at the same DC potential, and
> keep it there when voltage gradually builds in a storm. In the case of a
> strike, the ground electrodes are all tied together, but with
> considerable inductance between the tower and the house. The chokes
> minimize the voltage and current that goes to the shack for strikes of
> moderate size. In the case of a strike, the inductance will cause some
> gradient between the tower and the house, but the current that equalizes
> that gradient is far less likely to go through your ham shack
>
> And, your installation meets NEC, which could be an issue if you have
> real damage.
>
>