Topband: Best Outlet sttrip
Paul Christensen
w9ac at arrl.net
Wed Oct 9 10:02:35 EDT 2013
> "First, in most NA power systems, neutral and ground are connected at only
two places: (1) the secondary of the utility company's transformer; and (2)
> at the premises main panel board."
Sorry, should have read "...neutral and ground are connected *together* at
only two places..."
Paul, W9AC
----- Original Message -----
From: "Paul Christensen" <w9ac at arrl.net>
To: "TopBand" <topband at contesting.com>
Sent: Wednesday, October 09, 2013 9:55 AM
Subject: Re: Topband: Best Outlet sttrip
>> I'm afraid I don't understand how a surge
>> protector that clips an, e.g., 1KV spike on a 120 VAC line can end up
>> doing more damage than no protection all. I understand that the
>> clipped current pulse returns through the ground line and will cause a
>> voltage spike on the ground, and I also understand that other
>> interconnected equipment connected to different grounds may
>> potentially see part of the spike, but on balance that seems to me to
>> be a less dire situation than having no protection at all.
>
> I think it comes down to the surge protection device (SPD) wiring
> configuration in relation to its placement in the electrical system.
> First, in most NA power systems, neutral and ground are connected at only
> two places: (1) the secondary of the utility company's transformer; and
> (2) at the premises main panel board. An SPD, if used, should first be
> placed at either the electric meter or panel board so that surge currents
> near the utility entrance may divert on a short path to ground/neutral.
>
> On a branch circuit, the problem potentially becomes worse the further the
> distance of a common secondary SPD from the main panel (so-called "3 modes
> of protection" from devices using three MOVs). Surge currents being
> induced from say...a shack entry point can divert a large current onto the
> grounding conductor, causing a large voltage differential to other
> grounding points on the same branch circuit. On a branch circuit, surge
> current should never be diverted to a grounding conductor. It may be
> safely diverted to the neutral conductor and even then, it's best managed
> if at least a portion of the surge potential can first be stored and then
> "bled" onto the neutral where that neutral is connected to ground at the
> main panel. Common secondary protection SPDs meant for use on branch
> circuits don't meet this requirement, despite IEEE's recommendation that
> common "3 modes of protection" are safe for use on a branch circuit.
> Secondary SPDs that do accomplish this goal are made by BrickWall,
> ZeroSurge, and SurgeX.
>
> In a nutshell, my recommendation (for what little it's worth) is this:
> (1) a secondary SPD on a branch circuit should only be used when a primary
> SPD is used at the utility company's meter or at the premises main panel;
> and (2) assuming condition 1 is met, then the secondary SPD should divert
> surge current only onto the neutral, and never the grounding conductor.
>
> Finally, on the issue of balanced audio: it costs manufacturers of
> consumer electronics and ham gear no more to balance all audio inputs with
> a "3-stage" instrumentation op-amp circuit. It's far more important to
> balance each input this way than to balance audio outputs although
> balanced outputs are preferred for best system matching, especially on
> long cable runs or where distribution is complex (e.g., a broadcast or
> recording studio with cross-point switchers). With a true instrumentation
> input, the input circuit does not care if the source is balanced or
> unbalanced. It's simply a two terminal, floating device with extremely
> high common-mode rejection (CMRR) performance. The best laid out
> instrumentation circuits carry that high rejection well into the HF range.
>
> Paul, W9AC
>
>
>
>
> _________________
> Topband Reflector